    Good day all,

    I am currently busy with alterations at a small factory that is in the proses of being sold and would also require a CoC. While working a came across this neutral(50mm) in the SUB DB which has its stands split and connected independently to the neutral bar due to the fact that the neutral bar cannot accommodate the size.
    I would like to know if this is acceptable and where it states in SANS?
    I have located the previous electrician that did this job and he says its acceptable because the size of the neutral is not reduced.

    Any input?

    Thanx
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG_20180109_174245.jpg 
Views:	625 
Size:	35.4 KB 
ID:	6970  

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Yeah, I've also come across some pretty creative solutions to terminating oversize wiring in the past as well. Clearly if the wire won't fit in the hole then it will be contrary to the manufacturers specifications for that product to terminate it.
    I can't tell the dimensions of the neutral bar from the photo but if it's 7x9mm then the max current is usually 60 or 70 Amps, 8x12mm is normally limited to 100A (from memory) so if the wiring is 50mm˛ then there's also a good chance the neutral bar is also undersized for the OCPD in the DB.
    My take on it is it's not compliant as it is but if you can find a 50mm pin lug or maybe a palm lug that will fit in the hole without butchering it first and if the neutral bar is current rated to same or greater than the main breaker then you might be in with a shout.
    Name:  images.jpg
Views: 1966
Size:  3.5 KB
    _______________________________________________

    _______________________________________________

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Hi

    SANS 10142 Ed 2 pg 137 - 6.3.7.2 c - Joints and terminations shall not allow the strands of a stranded conductor to spread

    That reg should solve any argument

  4. #4
    Full Member
    Join Date
    Jun 2016
    Location
    Port Elizabeth
    Posts
    28
    Thanks
    0
    Thanked 1 Time in 1 Post
    Hi,

    Thanks a lot guys, this will surely help.
    Will inform the owner and the person that has done this work to correct it at his own expense .

    Thanx

  5. #5
    Full Member
    Join Date
    Aug 2018
    Location
    pretoria
    Posts
    35
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Good day all
    If I may ask a question concerning the split neutral
    When a manual change over for a single phase generator is installed.the db is split and the essential circuits are supplied with it's own neutral bar .when gen is on then neutral comes to it fine.when it changes back to mains. It's neutral now from mains.am I not understanding but the gens neutral will have a bridge with the mains neutral.if so .is this correct? Please educate me
    Thank you

  6. #6
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by BEVIN View Post
    Good day all
    If I may ask a question concerning the split neutral
    When a manual change over for a single phase generator is installed.the db is split and the essential circuits are supplied with it's own neutral bar .when gen is on then neutral comes to it fine.when it changes back to mains. It's neutral now from mains.am I not understanding but the gens neutral will have a bridge with the mains neutral.if so .is this correct? Please educate me
    Thank you
    No.

    There's no bridge between Eskom and generator neutrals.
    Thats what the changeover switch is for.
    The installation gets either an Eskom neutral OR neutral from generator.
    The changeover switch sees to it that both cannot be simultaneously connected.
    Either one OR the other.

  7. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    My advise to you, find someone who understands the power produced by a generator. You need to understand the voltage output, if and when you need to bond the neutral and earth and if you require an earth spike and all that stuff.

  8. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    @BEVIN

    Refer to diagram P.2 on page 325 of SANS 10142-1:2020 Edition 3.

    Pay attention to the change over switch.
    The switch is shown in the "main supply on" position. You will notice that the neutral from the generator is isolated.

    There's your answer.

    In the older reg book, the diagram can be found on page 357.

    Hope this helps, my brother.

  9. #9
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    @Bevin.

    Also take note of what it says just above the change over switch.

    I quote "change - over switch to break all live conductors including neutral"

Similar Threads

  1. Neutral leaking 220V to Earth
    By Etienne Swanepoel in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 19-Oct-14, 07:37 PM
  2. [Question] Equity split
    By Nickolai Naydenov in forum Entrepreneurship and Business Management Forum
    Replies: 5
    Last Post: 07-Aug-13, 09:36 PM
  3. The value of split-testing
    By Norri in forum Marketing Forum
    Replies: 5
    Last Post: 22-Jun-12, 02:18 PM
  4. [Question] What happens when 2 CC directors split up?
    By Dave D in forum General Business Forum
    Replies: 10
    Last Post: 24-May-12, 04:07 PM
  5. Cronin's comments on alliance split
    By duncan drennan in forum General Business Forum
    Replies: 3
    Last Post: 29-Jun-06, 07:58 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •