Depends on the circuits in the SubDB. If there's socket circuits or any other types of circuit that require earth leakage protection then yes, there should be an earth leakage breaker installed (or RCBO's used instead of MCB's).
No, highly unlikely. We work on a system of 'diversity' where it's assumed (gambled) that every circuit would never simultaneously be under full load conditions. There are rules for working out diversity in the regs.
It's poor electrical design to have an earth leakage breaker that's fed from another earth leakage breaker unless one is differently rated to the other ie one is a faster type or they both have different mA ratings otherwise it's always a lottery which one trips first and often both will trip during a fault. It's also bad design to have the supply for a SubDB run from an earth leakage breaker in the main DB.
_______________________________________________
_______________________________________________
Dave A (20-Sep-17)
It's poor electrical design to have an earth leakage breaker that's fed from another earth leakage breaker unless one is differently rated to the other ie one is a faster type or they both have different mA ratings otherwise it's always a lottery which one trips first and often both will trip during a fault. It's also bad design to have the supply for a SubDB run from an earth leakage breaker in the main DB.
- Does this mean that A sub DB board is wired in parallel to the main board rather than being fed off the main db board breaker - so that each board has its own separate supply, main breaker and earth leakage?
Why are the two breakers in series with the same break current?
Which one will break if a fault occurs in the garage at 60A?
This was just a drawing I had kicking around so I edited it for illustration.
The garage circuit breaker would be sized according to the size of cable feeding the garage and several other factors including the installation method used for the cable and the length of the cable etc.
It could be okay to use the same size breaker for the garage as the main breaker if the cable size was sufficient but it would be good practice to introduce 'discrimination' by making the garage breaker a faster curve than the main breaker ie the garage breaker might be a 'B curve' and the main breaker could be a 'C curve'.
0600DB0105.pdf (first page for brief explanation)
_______________________________________________
_______________________________________________
What non-electrical people need to understand is that a circuit breaker is selected to match the thickness of the wire used along with other factors. It's purpose is to protect that cable. Usually in the main DB the breaker is stronger for the supply to a sub-DB because the cable is thicker. The sum of the breakers is never a consideration. Many sub-DBs' have a supply rated at below 60A in the main board, but the main switch in the sub-DB is rated at 60A. This is because a 60A Double pole isolator is cheaper. The pupose of the main switch is to isolate the sub-installation. Each circuit fed from the sub-DB should be protected by a lower rated CB than the Sub-DB supply CB in the main board. This will localise tripping to the sub-DB.
The only device in the DB that protects the user is the ELCB. It is good practice to once a month switch off all electronic devices and press the test button on the ELCB. This will be an indication that it it still functioning. It is also wise to have it tested every two years to determine whether it still functions within the rating.
If the Sub-Db is fed from the main breaker Pre-Earth Leakage in the main DB, does this mean that the cable from the main DB to the garage sub-DB is not protected by an earth leakage device and that only the wiring and devices after the Sub-DB's earth leakage device are protected by the EL? Is the cable from the main DB to the Sub-DB only protected from over-current by the MCB and not protected against earth leakage?
Could one, for example, have the EL for the sub-DB situated in the main DB enclosure as shown in this diagram?
![]()
One could have the sub db fed from the earth leakage in the main db as in the diagram, however, I never do it that way. I always ensure that the sub db has it's own earth leakage. That way, if there's an earth fault on the sub db, it doesn't affect the main db.