Go do a refresher course with the ECA or the like...then you will realise why the industry is so F^&%*.
I was called out yesterday to assist with a circuit breaker tripping problem. A new machine was installed and the breaker kept tripping...
A CBI curve 3...30 amp 3 ka breaker installed in a factory. These breakers are designed for DOMESTIC installations, not industrial. Mixing various ka ratings of circuit breakers is quick way of identifying that the electrician who is installing the breakers is clueless.
D...1 and 2 curve circuit breakers are NOT DESIGNED TO BE USED FOR A/C UNITS ONLY...yesterday when i advised the electrician that he had installed the incorrect breaker...his response " orange curve 1 breakers are only used for A/C units...BULLSHIT.
A message to all electricians.......if you work in an commercial or industrial environment go do your homework on circuit breaker selection before you make a fool yourself... Just like installing cables...running 2 cables is not always the solution to high current especially if the equipment is close to the transformer...the fault level has to be taken into consideration for both the cable and the circuit breaker.