    Compliance of electrical wiring in ceiling space

    Kindly comment if the wiring done as per the images are compliant.

    Click image for larger version. 

Name:	electric wiring 1.jpg 
Views:	2556 
Size:	58.0 KB 
ID:	6730Click image for larger version. 

Name:	electric wiring 2.jpg 
Views:	3453 
Size:	49.7 KB 
ID:	6731

  2. #2
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Unfortunately, while poorly done it is not illegal. The cables are not on hot water pipes and the joints are enclosed.

  3. #3
    Full Member
    Join Date
    Jul 2015
    Location
    Cape town
    Posts
    46
    Thanks
    18
    Thanked 5 Times in 5 Posts
    in fact it usually looks worse, that's one of the better jobs we see lol

  4. #4
    Full Member
    Join Date
    Sep 2018
    Location
    Johannesburg
    Posts
    41
    Thanks
    0
    Thanked 2 Times in 2 Posts
    But the wires suppose to run into plastic pipes i think ?

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,228
    Thanks
    34
    Thanked 302 Times in 256 Posts
    No need for Twin and earth to run in conduit within the roof space

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The only thing I can see that's not compliant is the proximity of the conduit box to the lamp in the downlight but if it's LED even that isn't an issue. Maybe lack of strain relief for the connection in the conduit box but as already stated whilst it's an untidy installation it's not illegal.
    _______________________________________________

    _______________________________________________

  7. #7
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by AndyD View Post
    Maybe lack of strain relief for the connection in the conduit box
    If there is a gland on the underside of the conduit box that provides adequate strain relief for the connections within the conduit box then I would say its compliant.
    If there is no gland however I would fail it.

    Something else is that there is more than one cable in some of the glands. I read a long time ago in the regs, and now I cannot find it, that each piece of equipment must be utilised as It was originally intended. I am sure that this means there should only be one cable per gland
    Last edited by Leecatt; 03-Oct-18 at 05:48 AM. Reason: Spelling
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  8. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by Leecatt View Post
    .....Something else is that there is more than one cable in some of the glands. I read a long time ago in the regs, and now I cannot find it, that each piece of equipment must be utilised as It was originally intended. I am sure that this means there should only be one cable per gland
    You could go one stage further and fail glands with a stuffing rubber that has a round hole when there's a flat twin cable going through it because officially you should use one of these with an oval shaped hole;
    Name:  1.jpg
Views: 5677
Size:  7.8 KB


    I see where you're coming from but I'm not usually quite that pedantic to be honest, if there's a gland or an alternative entry system and it's maintaining the IP level and providing reasonable strain relief I wouldn't fail it.
    _______________________________________________

    _______________________________________________

  9. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The only thing wrong in the pic, the twin and earth is running on top on the beams. The twin+e is not protected on the beams, any person working in the roof space could damage the wire and expose the live conductors. I am sure you could find a clause in the SANS if you really looked and interpreted it a way to point this out. What you would then do with the info is the part that makes me laugh at this industry. It is like trying to tell a taxi boss his body guards are not allowed to carry full automatic weapons like and AK 47. I dare you to waste the time and energy.

  10. #10
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Evening all

    The cables in question should be fixed at the ends to prevent strain as per the regulation 6.4.3.4

Page 1 of 2 12 LastLast

Similar Threads

  1. Electrical compliance certificate
    By ericlowry in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 23-Jul-13, 08:08 AM
  2. The new electrical certificate of compliance
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 23
    Last Post: 27-Sep-12, 11:34 AM
  3. electrical certificate of compliance
    By murdock in forum General Business Forum
    Replies: 13
    Last Post: 02-Jul-10, 09:13 PM
  4. Ceiling insulation effect on electrical work
    By duncan drennan in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 16-Jan-10, 05:04 PM
  5. Electrical Compliance Problems
    By Marq in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 24-Jul-08, 07:44 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •