    Fixed appliances

    What is the regulations saying with regards to three phase and single phase cooking appliances used in take away stores for example that is feed from a welding socket? The socket can also be classified as an isolator cause it serves the same perpose, but should it be on earth leakage or not? A fixed alliance don't need earth leakage protection cause its on an isolator but in this case its equipment thst s on wheels that can be moved for cleaning purposes due to the oil etc. I struggle to come to a solid point regarding this as there's so many points that almost sounds contradictory in sans 10142:1. And some equipment works on two phases and neutral but I haven't seen a 2 phase c\b except for live and neutral 2 pole circuit breakers and then the normal 3 pole circuit breakers. What's your opinion about this and issuing a coc for this kind of installation?

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Durban, South Africa
    Thanked 2,473 Times in 2,078 Posts
    Blog Entries
    When it comes to socket-outlets, section 6.15 must be taken into account. contains this -
    NOTE 1 Dedicated socket-outlets are the only socket-outlets that need not be protected by earth leakage.
    Then contains this -
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove coupler is used.
    The use of the term "stove coupler" may cause some confusion (as it did during the interview of one of the candidates for a technical advisor post of the ECA(SA) last week), so for clarity - specifies -
    A stove coupler shall comply with the requirements of SANS 60309-1 and shall be of dimensions as given in SANS 337.
    The trouble with opportunity is it normally comes dressed up as work.

    Alcocks | Electrical Services | Hygiene Services & Washroom Products | Pest Control & Entomological Services

Similar Threads

  1. Isolators for Fixed Appliances
    By BlueArc in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 03-Feb-17, 08:03 AM
  2. Kitchen appliances - recommendations?
    By Basment Dweller in forum General Business Forum
    Replies: 28
    Last Post: 02-Oct-14, 06:10 PM
  3. 110VAC 60Hz Appliances from USA
    By douw in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 30-Jan-13, 05:55 PM
  4. gas appliances
    By murdock in forum General Chat Forum
    Replies: 17
    Last Post: 28-Jul-11, 08:28 AM
  5. bathrooms and fixed appliances
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 27-Jun-11, 07:03 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts