Page 3 of 4 FirstFirst 1234 LastLast
Results 21 to 30 of 40

Thread: Issuing electrical COCs - On a hiding to nothing!

  1. #21
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,673
    Thanks
    3,313
    Thanked 2,677 Times in 2,259 Posts
    Blog Entries
    12
    Quote Originally Posted by Sparks View Post
    An eyelevel oven with a hob connected to it more than 1m away, the interconnecting cables form part of the COC. The COC does not end at the first point of termination. The actual oven and hob however are still not part of the COC.

    The connecting cables of a split unit aircon unless mounted back to back will also qualify.
    Does this mean it can't be done in cabtyre exceeding a certain length?
    (3 metres)?

  2. #22
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    902
    Thanks
    21
    Thanked 127 Times in 96 Posts
    It means that where integral wiring exceeds 1m in length, that integral wiring also forms part of the certifiable installation and must comply with the applicable regs.

  3. #23
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    aircons are a good example...they use to only use cabtyre...but inoticed on the project we are busy with they are using 2.5 x 4 core surfix

  4. #24
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,673
    Thanks
    3,313
    Thanked 2,677 Times in 2,259 Posts
    Blog Entries
    12
    Quote Originally Posted by Sparks View Post
    It means that where integral wiring exceeds 1m in length, that integral wiring also forms part of the certifiable installation and must comply with the applicable regs.
    I've just raised this with my wireman and he's scratching his head - there's nothing about this in the airconditioning section of fixed appliances.
    What is the applicable reg?

  5. #25
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts

    Smile

    Quote Originally Posted by Dave A View Post
    I've just raised this with my wireman and he's scratching his head - there's nothing about this in the airconditioning section of fixed appliances.
    What is the applicable reg?
    1./ I understand the following to mean that the wiring between different parts of the same appliance that exceed 1,5 meters are to be considered as part of the electrical installation and subject to SANS requirements:

    6.16.1.1 Fixed appliances do not form part of the electrical installation other than their positioning in relation to the supply and the wiring carried out between different parts of the appliances.

    6.16.1.11 The wiring between different parts of a fixed appliance that are installed separately is part of the fixed installation, even where it is supplied from a socket-outlet, unless such wiring is less than 1,5 m in length.


    2./ I understand the following to mean that 2.5mm and 1.5 mm cables should be solid copper type. Ie Surfix or Norsk cable.

    6.3.2 Construction
    6.3.2.1 Conductors of nominal cross-sectional area exceeding 2,5 mm2 shall be stranded, except in the following cases, where solid conductors may be used:
    a) conductors of mineral-insulated metal-sheathed cables;
    b) internal connections of distribution boards, switchgear and industrial
    controlgear;
    c) busbars;
    d) aerial conductors;
    e) aluminium conductors of nominal cross-sectional area 16 mm2 or
    more; and
    f) copper conductors of nominal cross


    3./ I understand the following to exclude the use of Cabtyre cables entirely

    6.3.1 Materials
    All conductors of nominal cross-sectional area less than 16 mm2 shall be of annealed copper. In the following cases alternative material may also be used:
    a) earth continuity conductors (see 6.12.1.9);
    b) bonding conductors (see 6.13.1); and
    c) aerial conductors (see 6.3.4).


    4./ I hope that I have understood the above quotes correctly.
    The reason I am here is to learn and not to teach, please criticize if necessary.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  6. Thanks given for this post:

    Dave A (13-Feb-12)

  7. #26
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,673
    Thanks
    3,313
    Thanked 2,677 Times in 2,259 Posts
    Blog Entries
    12
    Thanks Leecatt. At least I can now point to the relevant section that drives the point raised.

    While I was looking at the section myself, it struck me how easy it is to take stuff out of context. As example:

    6.16.1.6: A socket-outlet shall supply only one fixed appliance. The use of flexible cords of length exceeding 3 m is not recommended.

    It's clearly pretty important to pay attention to the whole section to get the right interpretation (in this case 6.16.1.1 to 6.16.1.13 in full by the looks of things).

  8. #27
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    and you need to understand the different between cabtyre flexible cords and and flexible cables...i went to a site where the cabling between the floors...where wired with flexible cables...which was not illegal because unless you understand the definition of cords and cable you could make a noise for nothing.

  9. Thanks given for this post:

    Dave A (13-Feb-12)

  10. #28
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by Dave A View Post
    Thanks Leecatt. At least I can now point to the relevant section that drives the point raised.

    While I was looking at the section myself, it struck me how easy it is to take stuff out of context. As example:

    6.16.1.6: A socket-outlet shall supply only one fixed appliance. The use of flexible cords of length exceeding 3 m is not recommended.

    It's clearly pretty important to pay attention to the whole section to get the right interpretation (in this case 6.16.1.1 to 6.16.1.13 in full by the looks of things).
    Thats right, you literally have to know the whole book - in context as well.
    I must be honest and say that I enjoy the rules and regs, quirky but that's me.
    I find that the older I get the more slips away and its not that easy any more so this forum is something of great value to me.
    If I go on too much about SANS feel free to shit me out

    By the way, the name is Lee (i dont know how to change the LEECATT?)
    Last edited by Leecatt; 13-Feb-12 at 09:05 PM. Reason: additional info
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  11. #29
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,927
    Thanks
    577
    Thanked 936 Times in 757 Posts
    Quote Originally Posted by Leecatt View Post
    3./ I understand the following to exclude the use of Cabtyre cables entirely

    6.3.1 Materials
    All conductors of nominal cross-sectional area less than 16 mm2 shall be of annealed copper. In the following cases alternative material may also be used:
    a) earth continuity conductors (see 6.12.1.9);
    b) bonding conductors (see 6.13.1); and
    c) aerial conductors (see 6.3.4).

    I don't think that 6.3.1 excludes the use of cabtyre. Cabtyre has stranded annealed copper conductors. I think section 'a' allows earthing continuity conductors to be galvanised steel conduit for example. Section 'b' allows bonding conductors to be hard-drawn copper bar (not annealed) or aluminium.

    I completely agree that interconnecting cables for an oven/hob or an airconditioner may fall under the COC and simple running these appliances from a plug wouldn't exclude them.
    _______________________________________________

    _______________________________________________

  12. #30
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,673
    Thanks
    3,313
    Thanked 2,677 Times in 2,259 Posts
    Blog Entries
    12
    Yet another opportunity to be slagged off as money-grubbing rip-off artists by the the looks of things.

    But as I keep saying to clients in our defence - we don't make the rules, we just apply them.

    Quote Originally Posted by Leecatt View Post
    By the way, the name is Lee (i dont know how to change the LEECATT?)
    I just checked - I regret the username Lee is already taken.

Page 3 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. Electrical Compliance Problems
    By Marq in forum Electrical Contracting Industry Forum
    Replies: 11