It means that where integral wiring exceeds 1m in length, that integral wiring also forms part of the certifiable installation and must comply with the applicable regs.
aircons are a good example...they use to only use cabtyre...but inoticed on the project we are busy with they are using 2.5 x 4 core surfix
Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services
1./ I understand the following to mean that the wiring between different parts of the same appliance that exceed 1,5 meters are to be considered as part of the electrical installation and subject to SANS requirements:
6.16.1.1 Fixed appliances do not form part of the electrical installation other than their positioning in relation to the supply and the wiring carried out between different parts of the appliances.
6.16.1.11 The wiring between different parts of a fixed appliance that are installed separately is part of the fixed installation, even where it is supplied from a socket-outlet, unless such wiring is less than 1,5 m in length.
2./ I understand the following to mean that 2.5mm and 1.5 mm cables should be solid copper type. Ie Surfix or Norsk cable.
6.3.2 Construction
6.3.2.1 Conductors of nominal cross-sectional area exceeding 2,5 mm2 shall be stranded, except in the following cases, where solid conductors may be used:
a) conductors of mineral-insulated metal-sheathed cables;
b) internal connections of distribution boards, switchgear and industrial
controlgear;
c) busbars;
d) aerial conductors;
e) aluminium conductors of nominal cross-sectional area 16 mm2 or
more; and
f) copper conductors of nominal cross
3./ I understand the following to exclude the use of Cabtyre cables entirely
6.3.1 Materials
All conductors of nominal cross-sectional area less than 16 mm2 shall be of annealed copper. In the following cases alternative material may also be used:
a) earth continuity conductors (see 6.12.1.9);
b) bonding conductors (see 6.13.1); and
c) aerial conductors (see 6.3.4).
4./ I hope that I have understood the above quotes correctly.
The reason I am here is to learn and not to teach, please criticize if necessary.
To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.
Dave A (13-Feb-12)
Thanks Leecatt. At least I can now point to the relevant section that drives the point raised.
While I was looking at the section myself, it struck me how easy it is to take stuff out of context. As example:
6.16.1.6: A socket-outlet shall supply only one fixed appliance. The use of flexible cords of length exceeding 3 m is not recommended.
It's clearly pretty important to pay attention to the whole section to get the right interpretation (in this case 6.16.1.1 to 6.16.1.13 in full by the looks of things).
Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services
and you need to understand the different between cabtyre flexible cords and and flexible cables...i went to a site where the cabling between the floors...where wired with flexible cables...which was not illegal because unless you understand the definition of cords and cable you could make a noise for nothing.
Dave A (13-Feb-12)
Thats right, you literally have to know the whole book - in context as well.
I must be honest and say that I enjoy the rules and regs, quirky but that's me.
I find that the older I get the more slips away and its not that easy any more so this forum is something of great value to me.
If I go on too much about SANS feel free to shit me out
By the way, the name is Lee (i dont know how to change the LEECATT?)
Last edited by Leecatt; 13-Feb-12 at 09:05 PM. Reason: additional info
To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.
I don't think that 6.3.1 excludes the use of cabtyre. Cabtyre has stranded annealed copper conductors. I think section 'a' allows earthing continuity conductors to be galvanised steel conduit for example. Section 'b' allows bonding conductors to be hard-drawn copper bar (not annealed) or aluminium.
I completely agree that interconnecting cables for an oven/hob or an airconditioner may fall under the COC and simple running these appliances from a plug wouldn't exclude them.