As 6.16.4.1.1 is entirely silent on space heating and cooling appliances that are rated at less than or equal to 16A, the clause is largely irrelevant when it comes to determining the isolator requirements for such appliances. It is also worth mentioning that the primary point introduced by the clause is the provision of dedicated circuits - the consequences on the arrangement of isolators is effectively secondary.
The hurdles to overcome generally when it comes to isolators for fixed appliances lie in 6.16.1.
6.16.1.3 The power supply to every fixed appliance, except luminaires, shall be supplied through
a) a disconnecting device that disconnects both live conductors in a single-phase supply and all phase conductors in a multiphase supply, or
b) a socket-outlet
that is directly accessible...
6.16.1.5 The disconnecting device shall be positioned
a) within 1.5 m from the appliance, or
b) in a distribution board (if the switch-disconnector is capable of being locked in the open position).
Even where a ...
Perhaps your electrician needs to explain how his proposed arrangement complies with these two foundation sections.