    Hi ,
    If one has existing surfix only through a house wall not a fire wall .(As per a thread on the forum . This is illegal.) Would the best way to rectify the problem be to disconnect and remove the surfix from the wall , drill and insert 20mm PVC conduit through the drilled hole , add a PVC elbow on either side of the wall to the 20mm conduit ,add 20mm pvc conduit to the elbows on both sides of the wall ,add a two way round box to the added 20mm conduit on both sides of the wall , add PVC glands to the two way round boxes on both sides of the wall , install the surfix cable through this setup. Would this be legal .How would one sort the problem out . Is there a better way to do this.

    How would this be done if the wall was a firewall like a wall separating a garage wall and lounge.

    I have had a look at the regs but cannot seem to find a suitable answer. It is more the practicality what can you use what can you not use , interpreting the regs and placing it all together .I am an electrician but found out I am not as clued up as I thought especially after reading this forum and looking at the regs . My speciality is more in other areas of electricity. I need to up my game . Where can one find decent resources on practical house wiring.

    thanks

  2. #2
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    where do you see that its illegal to go through the wall with surfix? if it is legal to be plastered into the wall then going through the wall is no different.
    im not sure where you can find more resources on house wiring. the forum is probably the best place.

  3. Thanks given for this post:

    Gtfast (20-Apr-16)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,932
    Thanks
    578
    Thanked 936 Times in 757 Posts
    Surfix can legally be installed '6.3.6.1 b. under plaster 6.3.6.1 d. in hollows (such as in walls and partitions) (no additional protection being needed),'. This would include a hole through a wall as far as I know. The only problems that arise are when the wall is a fire barrier by design.
    _______________________________________________

    _______________________________________________

  5. Thanks given for this post:

    Gtfast (20-Apr-16)

  6. #4
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    77
    Thanks
    34
    Thanked 1 Time in 1 Post
    I always understood one can wire surfix/twin and earth/multicore cables through a wall. Then I came across this regulation on the forum.

    Page 149:

    6.4.8 Wiring through building elements:

    6.4.8.1 If wiring has to pass right through a building element such as a
    floor, a wall, a partition, or a ceiling, conductors and busbars shall be in a
    non-flammable enclosure or wireway.

    Is my understanding wrong.

  7. #5
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    Masonry and bricks is a non-flammable "enclosure". See chimneys and braai places. a wood wall "enclosure" is flammable.

    http://www.ppc.co.za/media/18085/MSD...als-Safety.pdf
    Last edited by ACEsterhuizen; 19-Apr-16 at 03:34 PM. Reason: more info

  8. Thanks given for this post:

    Gtfast (20-Apr-16)

  9. #6
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    77
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thank you
    makes sense.
    In reg 6.4.8.2 it indicates a cable only through a building element if it is a fire break. In which case one would need to apply non flammable material around the cable.This would also indicate a cable only through a building.

  10. #7
    Platinum Member SilverNodashi's Avatar
    Join Date
    May 2007
    Location
    Johannesburg, South Africa
    Posts
    1,197
    Thanks
    12
    Thanked 188 Times in 136 Posts
    Quote Originally Posted by Gtfast View Post
    Thank you
    makes sense.
    In reg 6.4.8.2 it indicates a cable only through a building element if it is a fire break. In which case one would need to apply non flammable material around the cable.This would also indicate a cable only through a building.
    So, to answer your OP, no you don't need to install the PVC pipe, elbows and junction boxes - which would be destroyed in the fire in anycase and leave the whole open - defeating the purpose of the firewall The hole needs to be covered with a fireproof sealant, as far as a I know.

  11. Thanks given for this post:

    Gtfast (03-Jun-16)

  12. #8
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    77
    Thanks
    34
    Thanked 1 Time in 1 Post
    HI ALL
    As per this thread.
    Is running surfix on its own through wooden cupboard partitions legal.

    Thank you

    Sent from my ANE-LX1 using Tapatalk

  13. #9
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    77
    Thanks
    34
    Thanked 1 Time in 1 Post
    As per this thread.
    Is running surfix on its own through wooden cupboard partitions legal.

    See reg 6.3.6.1 and 6.4.8.1.


    Thank you


    Sent from my ANE-LX1 using Tapatalk

  14. #10
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    It must be ...everyone does it.
    Comments are based on opinion...not always facts....that's why people use an alias.

  15. Thanks given for this post:

    Gtfast (16-Jan-20)

Page 1 of 2 12 LastLast

Similar Threads

  1. Too many cables in conduit
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 31
    Last Post: 12-Mar-19, 09:02 AM
  2. [Question] Surfix through wall
    By ChrisH in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 15-Apr-16, 10:03 PM
  3. surfix
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 22-Oct-14, 01:06 AM
  4. Metal conduit argument
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 19-Jul-13, 11:11 PM
  5. surfix in hazardous areas
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 16-Feb-13, 09:14 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •