No, you wouldn't disconnect the supply N-E link which is on the council/Eskom supply side, the test is just made with the installation isolated. Many times you might not have access to this link, it could be in a locked cabinet or supply/metering panel. Also the whole idea is to confirm that the link is still in tact especially with PME supplies where an open circuit PEN conductor can be dangerous.