    Hi All

    I would just like some clarity on installing an earth leakage for welding plugs. Most manufacturers only make 2 pole and 4 pole earth leakages so how would a 3phase plus earth welding socket need to be connected as there is no neutral

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    You can usually use a 4-pole earth leakage breaker on a 3 phase circuit that has no neutral. One issue may be that the test button is using the neutral to create the imbalance to trip when it's pressed in which case it's not a suitable.

    Just as a side note, RCD's and welders are a notoriously problematic and can result in bad nuisance tripping due to the type of load a welder presents to the supply with harmonics , high inrush currents and spikes. What do the manufacturers instructions say about the supply requirements? Sometimes they recommend that no RCD is fitted. Can the circuit be installed without an RCD and still meet compliance requirements? If it can ie dedicated sockets etc I'd suggest a risk assessment and see if the RCD is necessary.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. [Question] Earth Leakage Confusion
    By ursi in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 09-Nov-15, 08:44 PM
  4. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM
  5. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •