You would need to install an earth spike along with indictor lights etc at the DB
The neutral will also need to be earthed but only when running on generator which can be done with a change over switch , switching neutral as well
If the genset is VOV it cannot be used and if you complete the installation correctly and the client then hooks up a VOV he will more than likely damage the generator
Pasted a couple of the regs below
7.12.2.7 A 230 V generator with a V-O-V earth connection (centre tap on
winding which is earthed), shall not be connected to a fixed electrical
installation.
NOTE Such a generator may be used as a free-standing unit to provide power to
specific appliances.
7.12.3.1 Neutral bar earthing
7.12.3.1.1 Protection in accordance with the requirements of 6.7 shall be
provided for the electrical installation in such a manner as to ensure correct
operation of the protection devices, irrespective of the source of supply or
combination of sources of supply. Operation of the protection devices shall
not rely upon the connection to the earthed point of the main supply when the
generator is operated as a switched alternative to the main supply.
Where there is no existing earth electrode installed in the electrical installation,
a suitable earth electrode may be installed in accordance with SANS 10199.
When installed, the electrode shall be bonded to the consumer's earth terminal
and to the earthing point on the alternate supply by a conductor of at least half
the cross-section of that of the phase conductor, but not less than 6 mm2
copper, or equivalent. This also applies to a single-phase supply (see
also 5.2.3.1).
7.12.3.1.3 Where alternative supplies are installed remotely from the
installation, or from one another, and where it is not possible to make use of
a single neutral bar or neutral conductor which is earthed, the neutral of each
unit shall be earthed at the unit and these points shall be bonded to the
consumer's earth terminal (see 6.12.4). The supply from each unit which
supplies the installation or part of the installation, shall be switched by means
of a switch that breaks all live conductors operating substantially together (see
figures P.2 and P.4), to disconnect the earthed neutral point from the
installation neutral when the alternative supply is not connected (see also
6.1.6).