    Hi there

    Looked at an existing install for a friend of client of mine. They had solar inverter installed with with mains supply for when the sun isn't shining. Basically when the sun is shining the solar panels charge the batteries, if the sun is not out the mains charges the batteries (after load shedding). The power goes to a sub DB (from the man DB) in 6mm flat twin and earth, through 30 amp breaker to the inverter and back to the sub DB through an earth leakage before going to 4 x 20 amp circuit breakers feeding 2 sockets each. The earth leakage sometimes trips, even when nothing is plugged in. The socket circuits were tested (earth, ins res, polarity) and all good, I tested the earth leakage to see if was oversensitive and it didn't trip. I found that the voltage coming out of the inverter to the earth leakage is 230 L-N, 180 volt(+/-) L to E and 50 volt(+/-) N - E. Even when I completely disconnect the out going cables from the inverter I still get these unusual voltages at the out put terminal of the inverter. I have triple checked with 3 different meters (2 major techs and a fluke 1653B) and still the same. The neutral bars are separate in the sub DB, one for the supply into the DB and supply out to the DB the other for the earth leakage protected circuits.

    If I do a Earth leakage test it doesn't trip when in the sub DB, which is because of these strange voltages. If i take the same earth leakage and test at my own home, it trips at 24mA perfectly.

    Contacted suppler and suggested that I link Neutral and Earth of the out going terminal and install an earth spike on the outgoing side. This sounds like a very bad idea to me. I get linking N and E on a generator but that operates when the the supply is completely disconnected via change over switch

    I have never had this before from an inverter. Surely should be 230 L - E, 240 L - N and pretty much 0V N -E

    What do you guys think, faulty inverter?

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Note that an inverter is a supply on its own, and usually isolated from the batteries. If the inverter is a pure sine wave inverter, they use high frequencies to generate the sine wave, these high frequencies are in a realm of their own which causes certain components to react in different ways, and hence the voltages you have measured between L and Earth and Neutral and Earth. What leads me to think that the inverter manufacturers have inserted a very small value capacitor between N and Earth, to feed this high frequency voltage to earth. This is common practice in switch mode power supplies, and with personal PCs I am sure that you have felt this tingling feeling when you touch your PC case and earth, this is voltage that is residual and is created by the high frequency electronics.

    If the supplier has suggested that you connect the inverter N and earth, then this is a good suggestion, as it now brings the inverter output floating supply to a known reference potential. If you feel concerned, then use a 1Amp fuse to test your system, between N and earth. If the fuse does not blow, and they pass your earth tests, then connect a wire instead of the fuse.

    We tend to forget that the ESKOM supply, transformer centre tap is connected to earth at the substation transformer, and that all connections connected to this are now referenced to earth by this connection. The inverters are a mini substation transformer, and therefor require that one of the floating wires is connected to earth.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    The inverter suppliers suggestion of knocking in an earth spike could be dangerous if you inadvertantly PME the Eskom supply when it's not a suitable existing earthing arrangement.

    Just a thought but check the connections at the inverter in case they've connected the cpc of the final circuit to the chassis of the inverter instead of the correct earth point or maybe there should have been a link between the earth from the incoming supply and a bonding terminal on inverter chassis.
    _______________________________________________

    _______________________________________________

  4. #4
    Bronze Member
    Join Date
    Oct 2014
    Location
    Pretoria
    Posts
    126
    Thanks
    16
    Thanked 16 Times in 15 Posts
    It is a requirement to do a earth neutral bridge at supply side. Only on supply side and not at consumer side.

    This is the same for generators and PV solar / inverters used as alternative supply.

    The requirement for earth spike is due to the fact that should the supplier's supply be disconnected the possibility of supplier earth also being disconnected is very high and thus using an alternative supply the possibility could be that no earth being available and thus be very dangerous as earth leakafe will not trip and floating voltages could be found on neutral.

    With earth spiking be attentive to the soil resistivity by conducting an earth resistance "earth spike" test.

    "I used to have a lot of anger issues, now I just have a passion for justice"

  5. #5
    New Member
    Join Date
    Aug 2019
    Location
    KZN
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi!

    Sorry for opening this old thread again!... I'm stuck with a similar problem as the original poster.

    I have a pure sine inverter/charger supplying the lights circuits in my house (-works fantastic for load shedding and other minor power failures). I connected the neutral wires of all the lights circuits to the neutral output of the inverter and isolated them. The system works fine - I sometimes don't even notice that there is an interruption of the municipal power supply... Recently I've anstalled some floor lights in the passage (very small, 2W LEDs) and then found that they won't switch off completely when the inverter is connected to mains. I asked the electrician to check it out and he informed me that the inverter is faulty as it has a high voltage reading between neutral and earth. After reading the discussion above, I decided to connect the inverter neutral out to the DB neutral bus. At first I thought it's working - when the lights are switched off, they are not dimmed, but completely off, but when I wanted to check the voltage between the neutral and earth, I realised that the inverter is running from the battery - the input fuse was blown.

    Any suggestions? I was considering isolating the neutral circuits again, but connecting them to the earth bus rather than the neutral bus in the DB, but I have only one spare fuse now ...

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Hi

    You need to ensure that the outgoing neutral and earth are common , bridged out.

    Bridging the incoming neutral to the outgoing neutral will create all sorts of problems - Think that is what you are saying

    Be careful and ensure that your neutral earth bridge does not earth the incoming neutral when running on mains

  7. #7
    New Member
    Join Date
    Aug 2019
    Location
    KZN
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks GCE for the advice! Yes, I tried bridging incoming and outgoing neutral and that caused the 2A fuse in the input to blow. Let me just get this clear ... bridging outgoing neutral and earth - this inverter has a 3-way output plug. Should I bridge Neutral and Earth inside this outlet plug? I'm pretty sure it's going to blow the fuse again, but I will give it a try and tell you what happens...

  8. #8
    Full Member
    Join Date
    Nov 2019
    Location
    Alberton
    Posts
    70
    Thanks
    2
    Thanked 4 Times in 4 Posts
    Hi JJF
    Have you ever resolved the 2A fuse that blew on inverter issue?

  9. #9
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Greetings All

    The regulations allows for the starting of the neutral and earth on the outgoing side of your alternative supply ( so all legal)

    If you get a reading between neutral and earth 9 times out of 10 it will be when the inverter is in battery mode or solar mode.

    I star the neutral and earth at the UPS Bypass switch (where the inverter output goes in)

    Not all inverters are designed to be wired directly into the DB so be cautious.

  10. #10
    New Member
    Join Date
    Aug 2019
    Location
    KZN
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Rifrug View Post
    Hi JJF
    Have you ever resolved the 2A fuse that blew on inverter issue?
    Sorry for only replying now! No, unfortunately I didn't get it resolved.

Page 1 of 2 12 LastLast

Similar Threads

  1. Inverter Install Compliance
    By deejaypsy in forum Electrical Contracting Industry Forum
    Replies: 43
    Last Post: 06-Mar-23, 07:14 AM
  2. Weird marketing
    By pmbguy in forum General Chat Forum
    Replies: 13
    Last Post: 22-Oct-13, 11:27 AM
  3. Difference between: Power factor correction, Voltage regulation and Voltage stabisizi
    By BigRed in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 08-Feb-10, 09:29 PM
  4. Battery + inverter advice required
    By daveob in forum Electrical Load Shedding Forum
    Replies: 12
    Last Post: 24-May-08, 04:05 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •