Results 1 to 10 of 44

Thread: Inverter Install Compliance

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Email problem Tonye's Avatar
    Join Date
    Mar 2015
    Location
    Pretoria
    Posts
    42
    Thanks
    0
    Thanked 11 Times in 8 Posts
    My bad. have changed diagram
    Click image for larger version. 

Name:	image.jpg 
Views:	2543 
Size:	80.6 KB 
ID:	5414

    One problem I had, was the inverter has a floating neutral on output side. Voltage tests between live & earth 110v, between neutral & earth 110v.
    Earth leakage on Mini DB showed an earth fault and would not trip.
    After consulting with an electrical engineer who stated the neutral needed a reference point, I connected the neutral to main earth on the output side of the inverter.
    Bingo, problem solved

  2. #2
    Full Member
    Join Date
    Jun 2012
    Location
    Plettenberg Bay
    Posts
    69
    Thanks
    1
    Thanked 17 Times in 13 Posts

    Smile

    Quote Originally Posted by Tonye View Post
    My bad. have changed diagram
    Click image for larger version. 

Name:	image.jpg 
Views:	2543 
Size:	80.6 KB 
ID:	5414

    One problem I had, was the inverter has a floating neutral on output side. Voltage tests between live & earth 110v, between neutral & earth 110v.
    Earth leakage on Mini DB showed an earth fault and would not trip.
    After consulting with an electrical engineer who stated the neutral needed a reference point, I connected the neutral to main earth on the output side of the inverter.
    Bingo, problem solved
    Ah hah!
    This solves a problem i have been finding of an earth fault not tripping the EL.
    So the solution is to earth the neutral on the load side(output) of the inverter?
    This makes sense.
    Thanx for the input.
    The inverters i have installed are line interactive inverters so no changeover switch is required. It switches automatically on mains fail, but even when Eskom is available it runs in bypass mode, still supplying the critical load with power at the rated maximum size of the inverter...

  3. #3
    Email problem Tonye's Avatar
    Join Date
    Mar 2015
    Location
    Pretoria
    Posts
    42
    Thanks
    0
    Thanked 11 Times in 8 Posts
    Glad I could help.

  4. #4
    Email problem Tonye's Avatar
    Join Date
    Mar 2015
    Location
    Pretoria
    Posts
    42
    Thanks
    0
    Thanked 11 Times in 8 Posts
    My inverters are also line interactive. The reason for running through the changeover switch is to allow the client to turn off
    Equipment which may overload the inverter.

  5. #5
    Email problem Tonye's Avatar
    Join Date
    Mar 2015
    Location
    Pretoria
    Posts
    42
    Thanks
    0
    Thanked 11 Times in 8 Posts
    Quote Originally Posted by deejaypsy View Post
    Ah hah!
    This solves a problem i have been finding of an earth fault not tripping the EL.
    So the solution is to earth the neutral on the load side(output) of the inverter?
    This makes sense.
    Thanx for the input.
    The inverters i have installed are line interactive inverters so no changeover switch is required. It switches automatically on mains fail, but even when Eskom is available it runs in bypass mode, still supplying the critical load with power at the rated maximum size of the inverter...
    Just completed an installation. Pulling my hair out. Earth leakage keeps tripping when running on inverter
    mode. Apparently their are different types of earth leakage units.
    Type AC, sensitive to alternating current only
    Type A, sensitive to alternating current and/or pulsating current with DC components.
    Don't know if you have also experienced this.
    Click image for larger version. 

Name:	image.jpg 
Views:	1299 
Size:	15.6 KB 
ID:	5477

  6. #6
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts
    What about a 2 pole circuit breaker on the inverter input and output side? And cable size on the AC side due to the charge current that the controller is set at?

Similar Threads

  1. Saturday at home, installing an inverter
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 241
    Last Post: 01-Feb-21, 09:50 AM
  2. How to install a prepaid meter for a flat ?
    By I.Sparks in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 15-Jan-14, 12:45 PM
  3. IE8 RC doesn't install in windows 7 beta
    By twinscythe12332 in forum Technology Forum
    Replies: 2
    Last Post: 22-Jan-09, 08:06 AM
  4. Battery + inverter advice required
    By daveob in forum Electrical Load Shedding Forum
    Replies: 12
    Last Post: 24-May-08, 04:05 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •