My bad. have changed diagram
One problem I had, was the inverter has a floating neutral on output side. Voltage tests between live & earth 110v, between neutral & earth 110v.
Earth leakage on Mini DB showed an earth fault and would not trip.
After consulting with an electrical engineer who stated the neutral needed a reference point, I connected the neutral to main earth on the output side of the inverter.
Bingo, problem solved