Page 7 of 9 FirstFirst ... 56789 LastLast
Results 61 to 70 of 88
Thread: Generator connection
  1. #61
    And if there is no center tap to earth?
    I can't help wonder if many of the gensets out there are not actually V-O-V with a center tap to earth, but actually "safe supply" arrangements.
  2. #62
    Jan 2016
    As I said (save for a few special builds) almost every generator under 7KVA is V-O-V (PNP). they are not designed for use as standby sets but rather as temporary supply via a lead. As long as your not connecting to the DB or feeding into the building supply in any other way these are legal, but the second you feed into the building they become illegal because there is no way you can bond the Neutral to the earth.
    What amasses me is that there are so many of these illegal installations, and they are being done by registered electricians and neither the ECA or the ECB have made any effort to stop this or to advice the public of the dangers.
  3. #63
    With respect, that doesn't answer the question.
    My 5.5 kVA generator doesn't have a center tap to earth.
    In fact there is no connection between the earth point of the generator and the single phase supply it provides. (Insulation test between earth and phase exceeds 1 Mega Ohm).
    Am I prohibited from connecting this generator to an electrical installation as an alternate supply?
  4. #64
    Jul 2008
    Germiston, South Africa
    I have been asked to connect up a generator which I have not seen yet and this was going to take place this morning.
    I have never connected a generator before because of the absolute minefield it has become, not to mention the confusion. However, I have taken an interest recently due to today's job and I am just wondering, are the regulations the same in version three of 10142—1 as they were in version 2, regarding the generator? I have yet to purchase version 3.
    Also,I noticed on the SABS website that there is a separate PDF available which deals entirely with the installation of generators. Has anybody purchased this separate PDF and and does it give clear concise instructions?
  5. #65
    Mar 2019
    East london
    Check your local municipality by laws as well.
    Here in our valley we need to apply and get permission from the Munic to do a generator installation.
    Technical specs of generator, circuitry and drawings of same are needed to accompany the application.
    Attached is a copy of our by laws, but I suggest you check those in your area before doing the job.
    https://www.buffalocity.gov.za/folder.php?id=sSWeUsCZg
    Peace out ... Derek.
  6. #66
    Besides a note added under 7.12.3.1.3 it is basically identical
    I have not seen the generator installation standard
    7.12.3.1.3 Where alternative supplies are installed remotely from the
    installation, or from one another, and where it is not possible to make use of
    a single neutral bar or neutral conductor which is earthed, the neutral of each
    unit shall be earthed at the unit and these points shall be bonded to the
    consumer's earth terminal (see 6.12.4). The supply from each unit which
    supplies the installation or part of the installation, shall be switched by means
    of a switch that breaks all live conductors operating substantially together (see
    figures P.2 and P.4), to disconnect the earthed neutral point from the
    installation neutral when the alternative supply is not connected (see also
    6.1.6).
    NOTE Where four pole switching is implemented, consideration should be given to use
    overlapping neutral switching devices
  7. #67
    Mar 2019
    East london
    Tested a generator this morning. The specific model ...... Ryobi rg 6900K.
    Results as follows:
    No load ..... L - N 235V ; L - E 160V ; E-N 75V
    With load .... L - N 235V ; L - E 235V ; E-N 0V
    Is there anyone who can explain this. I'm wracking what's left of my brain cells but cannot understand it.
    Peace out .. Derek
  8. #68
    Junior Member rh1's Avatar
    Dec 2017
    I am in Cape Town but a direct customer of Eskom, would COCT by-laws still apply to me?
  9. #69
    Jun 2020
    Fourways
    Results as follows:
    Peace out .. Derek
    Best guess is the voltage regulator stuff and perhaps a form of induced EMF on the N and E etc. A generator needs to run on load as far as I understand to run correctly.
    I have been told if a generator is producing more than the load it does not like it as it has to keep revs up and not stall but then too much voltage applied etc.
    Anyway that's my best so far as to why seeing voltages like that. Also then when it's under load then the genny i believe is then not VoV which is great
  10. #70
    Mar 2019
    East london
    @Dylboy. Yes, not vov for sure. I've checked if vov then the voltage is split 50/50 whether there is a load or not.
    Also, I cannot see 3 thick leads coming from the stator. Only 2, live and neutral. On vov wound, there are 3 thick leads coming from the stator with one of them (centre tap ) connected to earth.
    Gonna do more tests on Monday.
    Gonna connect it to installation and see if earth leakage works as it should.
    Peace out .. Derek
  1. 230 volt generator with a V-O-V earth connection
    Last Post: 29-Jul-20, 09:33 AM
  2. gas stove connection
  3. New Electricity Connection
    By elaine25 in forum Electrical Contracting Industry Forum
    Last Post: 27-Mar-14, 01:00 PM
  4. NETWORK CONNECTION PROBLEMS
    By Coolblue in forum Technology Forum
    Last Post: 07-Feb-13, 04:18 PM
  5. Internet connection speed
    By Martinco in forum Technology Forum
    Last Post: 11-Oct-12, 12:29 PM