    Hi All

    Following on the question raised by jvdh regarding the panel for controlling 2 pumps where the panel is considered part of the "machine" being the 2 pumps, the question arises:

    Does the control panel, housing circuit breakers, timer and a transformer for a domestic swimming pool also form part of the "machine" being the pool pump, or is it part of the installation ?

    Derlyn

  2. #152
    New Member
    Join Date
    Aug 2019
    Location
    Somerset-West
    Posts
    3
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thanks GCE for the reply..

  3. #153
    New Member
    Join Date
    Jul 2019
    Location
    Johannesburg
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi Derlyn
    The "panel" for a pool motor is actually a distribution board and is supplied by 220 volts, this then does not make the DB part of the "machine", so it must appear on the COC of the house being tested.
    Hoping that this helps you.
    Thanking you for the post.

  4. #154
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,264
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Hi Derlyn

    I had a conversation with an AIA over swim pool.
    He felt that the standard type swim pool "DB"would not pass the sans test as a DB and that he prefers to call it a Motor control centre (MCC) .
    If you install a weatherproof isolator and from the isolator feed the MCC you can regard the pool as a fixed apppliance .
    The fixed appliance would still need to be electrically safe to sign the COC

    The minute you take another light circuit or plug circuit from the MCC then it would become a DB

    I disagree with Mellet - A "Pool DB "need not automatically be a DB but could be a MCC

  5. #155
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by GCE View Post
    Hi Derlyn

    I had a conversation with an AIA over swim pool.
    He felt that the standard type swim pool "DB"would not pass the sans test as a DB and that he prefers to call it a Motor control centre (MCC) .
    If you install a weatherproof isolator and from the isolator feed the MCC you can regard the pool as a fixed apppliance .
    The fixed appliance would still need to be electrically safe to sign the COC

    The minute you take another light circuit or plug circuit from the MCC then it would become a DB

    I disagree with Mellet - A "Pool DB "need not automatically be a DB but could be a MCC
    A pool DB is a pool DB ...sold as a pool DB ...generally made up of a main switch...plug circuit feeding a plug socket (standard as per reg 164) which feeds what ever is plugged into it ...be it a pump motor...lawnmower (not suppose...however it is a reality)...etc...a light circuit sometimes feeding a transformer for a light in the pool or just general lights...very seldom supplied with an earth leakage unit (you would be required to connect it to the e/l unit in the in the DB it is fed from because of the standard socket outlet)

    However if you mounted a main switch/isolator ...motor control gear etc in a weather proof enclosure...mounted at the correct height (another issue with pool DB's)...feeding only a pump motor which has a weather proof isolator mounted within arms reach (not via a standard 16 amp socket outlet)...then we could start changing the name...as soon as you fit a light switch or standard socket ...you need to call a spade a spade.

    Building water treatment and waste water plants is a different ball game to domestic pool pumps...An MCC would be made up of a pump control section which is dedicated to power and control for the level control...valves...pumps...pumps etc and in some cases if general lighting and power is required...a separate compartment for a "DB" which would have the main switch...earth leakage and circuit breakers...which could be completely separate from the MCC.

    Pool DB's are another rats nest...the kind of issues i find is the DB is mounted to low...literally on the floor...too close to the pool...cables too small (many i have seen are fed via a 1.5 mm cable)...feeding gate motors...garden lighting...gazebos you name it.

  6. #156
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Greetings All

    If a extractor fan (kitchen) is on an earth leakage would you still require an isolator?

  7. #157
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,264
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Because an extraction fan is a motor , a motor has to have an isolator within a certain distance and 6.16.5.1.4 is relevant
    To me the isolating in a DB does not allow for the total removal of the appliance as stipulated in the same reg 6.16.1.4 and it actually contradicts itself.
    Using the ELU as the isolator would definitely not allow total removal unless that ELU was dedicated to the extractor only

    6.16.5.1.4 Each motor shall be supplied by a manually operated
    disconnector or any other manually operated disconnecting arrangement
    such as a withdrawable circuit-breaker, a removable link, a fuse or by the
    removal of a plug from a socket-outlet, which provides at least the same
    isolating distance, for the sake of safety, as a disconnector that is
    a) readily accessible and mounted on or next to the motor, or
    b) visible from the motor, or
    c) lockable in the open position, or
    d) housed in a lockable enclosure other than a distribution board
    .

    6.16.1.4 The disconnecting device shall be positioned
    a) within 1,5 m from the appliance, or
    b) in a distribution board (if the switch-disconnector is capable of being
    locked in the open position).
    Even where a disconnecting device is on the appliance, a separate
    disconnecting device shall be provided in the fixed installation to allow for the
    total removal of the appliance

  8. Thanks given for this post:

    SeanM (02-Sep-19)

  9. #158
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Evening GCE

    Thank you as always for the informative response.

    I was asking as in the regulations it says if a luminaire has a fan (motor) then an isolator must be fitted or it must be placed on an earth leakage, I am trying to understand the difference between a fan/motor on a luminaire and an extractor fan.

    I did a COC and the extractor fan (one with a chimney and a double storey so no ceiling) in the kitchen has no isolator and for me to fit one now would involve chasing not ideal and I want it to be first of all compliant and second of all neat.

  10. #159
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,264
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Hi Sean
    There is no neat way only the right way .

    I feel for you having to explain and it annoys me every time I have to explain and tell the owners ,"that I did not do it or make the rules , I just follow them "

  11. #160
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,524
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Hi Sean

    Does that extractor fan presently not get it's supply through a plug socket outlet ?

    If so, the socket outlet, if within 1,5 meters of the appliance, serves as the isolator.

    Derlyn

Page 16 of 29 FirstFirst ... 6141516171826 ... LastLast

Similar Threads

  1. [Question] Electrical Certificate of Compliance Number?
    By Herman in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 14-Mar-14, 12:23 PM
  2. Electrical compliance certificate
    By ericlowry in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 23-Jul-13, 08:08 AM
  3. The new electrical certificate of compliance
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 23
    Last Post: 27-Sep-12, 11:34 AM
  4. What are the Electrical Compliance Certificate Requirements
    By MikeS in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 18-Jun-12, 10:24 PM
  5. electrical certificate of compliance
    By murdock in forum General Business Forum
    Replies: 13
    Last Post: 02-Jul-10, 09:13 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •