There is no regulation stipulating the size of circuit required for a stove - Now a days with everyone going gas hob 25 amps is more than enough
If you are going to use all 4 plates , oven and warmer draw all at the same time then 25Amps may be to light
An oven is around 2 Kw which is 8 amps and once at temp comes on and off to maintain temp - a stove plate is +/- 1,5kw , around 6 amps
You can buy a stove that plugs into a normal socket
From SANS 10142-1 ed 3.1
6.16.3.2 Cooking appliance circuits
6.16.3.2.1 A dedicated circuit(s) shall be provided for cooking appliance(s)
that are rated at more than 16 A.