Quote Originally Posted by gautengaleng View Post
What's the required amps for a stove breaker switch? I'm buying an apartment and an electrician said by law he has to replace the switch from 25 amps to 40 or 50 (don't recall which). Sellers decided to send another electrician coz the first quote was too high. And this one says 25 amps is fine. So which is which?
There is no regulation stipulating the size of circuit required for a stove - Now a days with everyone going gas hob 25 amps is more than enough
If you are going to use all 4 plates , oven and warmer draw all at the same time then 25Amps may be to light

An oven is around 2 Kw which is 8 amps and once at temp comes on and off to maintain temp - a stove plate is +/- 1,5kw , around 6 amps

You can buy a stove that plugs into a normal socket

From SANS 10142-1 ed 3.1

6.16.3.2 Cooking appliance circuits

6.16.3.2.1 A dedicated circuit(s) shall be provided for cooking appliance(s)
that are rated at more than 16 A.