    Quote Originally Posted by dav View Post
    I have what is probably a dumb question, but what is the difference between an isolator and a disconnecting device?
    the other way of looking at it...a circuit breaker for example can be used as a disconnecting device if it has isolating properties for example a geyser combo breaker.

    andy i would be a bit cautious including a DOL starter...in some cases i have had been instructed that an emergency stop button connected to a DOL control circuit could not be used to isolate a circuit. I cant say for sure as it was an instruction i received from an electrical engineer...it would be an interesting topic to discuss.

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by ians View Post
    the other way of looking at it...a circuit breaker for example can be used as a disconnecting device if it has isolating properties for example a geyser combo breaker.

    andy i would be a bit cautious including a DOL starter...in some cases i have had been instructed that an emergency stop button connected to a DOL control circuit could not be used to isolate a circuit. I cant say for sure as it was an instruction i received from an electrical engineer...it would be an interesting topic to discuss.
    I suspect that the engineer stated this, as the disconnect, relies on a contactor to open its contacts.
    If the contactor housing or coil bobbin is damaged/distorted for what ever reason, it may impede the release of the contacts arm and opening the contacts.
    Also if the contacts have been welded due to a fault, then the release spring in the contactor may not have sufficient strength to physically break the electrical contact when the stop button is pressed.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Justloadit View Post
    I suspect that the engineer stated this, as the disconnect, relies on a contactor to open its contacts.
    If the contactor housing or coil bobbin is damaged/distorted for what ever reason, it may impede the release of the contacts arm and opening the contacts.
    Also if the contacts have been welded due to a fault, then the release spring in the contactor may not have sufficient strength to physically break the electrical contact when the stop button is pressed.
    that makes sense.

  4. #4
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    909
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Depending on the application I also use a socket outlet as an isolating device which is acceptable.

  5. #5
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    909
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Yes it may. Any new installation, alteration, extension or repair to an existing installation in some cases must be certified. Provided the rest of the installation is already covered by a valid COC.

  6. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Sparks View Post
    Yes it may. Any new installation, alteration, extension or repair to an existing installation in some cases must be certified. Provided the rest of the installation is already covered by a valid COC.
    If the COC was issued less than 2 years ago would you have to re inspect the installation to verify the COC is actually valid or just assume the installation is still reasonable safe and test the part of the installation you have done and attach the original COC

  7. #7
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    You're right Ian, DOL starter was a bad example, it may or may not qualify as an isolation device depending on its construction. The relevant standards for an isolation device are laid out in IEC 60947-3:2015, the SA standards authority adopted the IEC standard without any additions or alterations.
    _______________________________________________

    _______________________________________________

  8. #8
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    909
    Thanks
    21
    Thanked 127 Times in 96 Posts
    The chandelier is not a consideration unless there is a bowl over each lamp.

  9. #9
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    404
    Thanks
    25
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by ians View Post
    If the COC was issued less than 2 years ago would you have to re inspect the installation to verify the COC is actually valid or just assume the installation is still reasonable safe and test the part of the installation you have done and attach the original COC
    The only way to prove an existing Coc is valid is to inspect the installation, two years does not come into it.
    Theoretically and correctly, one should issue an additional Coc only if the existing Coc has been proven to be valid.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  10. #10
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    The UK domestic electrical industry falls under Part P legislation, commercial/industrial is different so in a nutshell you'd need to at least partly requalify then join a scheme in order to certify work unless you do so at a higher cost through building control. Have a look on the ELECSA / NAPIT / STROMA / NICEIC websites for more in depth info. http://www.elecsa.co.uk/Contractors/Part-P.aspx
    _______________________________________________

    _______________________________________________

Page 8 of 28 FirstFirst ... 67891018 ... LastLast

Similar Threads

  1. [Question] Electrical Certificate of Compliance Number?
    By Herman in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 14-Mar-14, 12:23 PM
  2. Electrical compliance certificate
    By ericlowry in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 23-Jul-13, 08:08 AM
  3. The new electrical certificate of compliance
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 23
    Last Post: 27-Sep-12, 11:34 AM
  4. What are the Electrical Compliance Certificate Requirements
    By MikeS in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 18-Jun-12, 10:24 PM
  5. electrical certificate of compliance
    By murdock in forum General Business Forum
    Replies: 13
    Last Post: 02-Jul-10, 09:13 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •