    Andy thanks for the explanation. Forgetting the strain relief, if the appliance had a earthing terminal (Class 1 appliance) it would then be a legal installation?
    I personally would say no it wouldn't be compliant unless the lampholder is covered and not accessible using the finger test. Please don't take my answer as definitive though because I'm not an electrician as such, I design and build control sytems.

    Quote Originally Posted by ians View Post
    Simple, Maizey plastics, clear perspex a little heat and 2 screws or just buy cheap plastic bulkheads and remove the clear covers and secure using the holes on the cover.

    If it is for your own house, take them out throw them in the dustbin and fit led strip lights.
    This would be the route I would go.

    I'm also assuming there's ballasts with open wiring and terminals somewhere.
    _______________________________________________

    _______________________________________________

  2. #12
    Full Member
    Join Date
    Jun 2014
    Location
    Somerset West
    Posts
    42
    Thanks
    3
    Thanked 5 Times in 5 Posts
    Quote Originally Posted by AndyD View Post
    I personally would say no it wouldn't be compliant unless the lampholder is covered and not accessible using the finger test.
    Found SANS 10142; 6.14.4.1: A lamp holder shall be shrouded in insulating material or shall be earthed, unless it is simultaneously:

    a) out of arm's reach
    b) ....

    I gather from this that it would be acceptable as long as no live conductors are accessible and the casing of the lamp holder is earthed?

  3. #13
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Busy with some emergency lighting, wow put a whole new twist on dangerous, having a permanent live and a switched live and just to add a whole pile of exposed wiring 😜clearly someone forgot to mention it to emergency backup companies.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #14
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Quote Originally Posted by AndyD View Post
    I'm also assuming there's ballasts with open wiring and terminals somewhere.
    Nope - 220v all the way to the CFL.

    Quote Originally Posted by PaulG View Post
    I gather from this that it would be acceptable as long as no live conductors are accessible and the casing of the lamp holder is earthed?
    Not an earth to be found, and to retrofit one to each light is going to get ugly.

    We've gone with the plastic bulkhead covers solution as suggested by Ian, which also resolves the concern that immediately leapt out at me from my food safety interests - containment if the bulb is broken. Nothing quite like shards of glass with your favourite tipple to test if you've had too much already.

  5. #15
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts

    Exposed wiring in home bar lighting

    Dave I have some bad news for you those lamps cannot run without a ballast, they must be some where hidden away.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #16
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    I thought the same but when Dave said no ballasts I assumed the lamp holder might have it integrated. I've not come across this but the lamp holder looks considerably deeper than usual so I'm not sure.
    _______________________________________________

    _______________________________________________

  7. #17
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Quote Originally Posted by AndyD View Post
    I thought the same but when Dave said no ballasts I assumed the lamp holder might have it integrated.
    Let's assume I'm wrong then.

    Please bear in mind my IE brings me the problem he's looking for opinions on - in this case the exposed wiring at the light. As a result my knowledge of the entire situation can safely be assumed to be incomplete, so the correct answer on ballasts would be "there's been no mention of ballasts as an issue."

Page 2 of 2 FirstFirst 12

Similar Threads

  1. [Question] Wiring under thatch
    By camrad in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 07-Sep-17, 05:32 AM
  2. Home Automation Wiring
    By mrmin24 in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 14-Mar-14, 09:56 AM
  3. headlines zuma family scandals exposed
    By murdock in forum South African Politics Forum
    Replies: 2
    Last Post: 06-Apr-12, 10:15 AM
  4. Vulnerability exposed
    By Dave A in forum Technology Forum
    Replies: 3
    Last Post: 05-Jan-07, 11:47 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •