    KA testing on UPS Supplies

    I have recently had to COC a socket outlet circuit in an existing installation. (The current one is a single 32A single phase industrial socket). This socket is the backup to server equipment via a UPS feed via a 20A 5KA S/P C/B. The problem I have is that the KA test and earth loop impedence test cannot be performed because it is fed from a UPS.

    How do you complete the COC in these circumstances.

  2. #2
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    just do the ka and loop test on the supply side at the d.b.

  3. #3
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    72
    Thanks
    0
    Thanked 5 Times in 4 Posts
    Yes I thought of that but the feed DB to the socket outlet is in a server / control room and is part of a large refinery. The DB (floor to ceiling 6 door cabinet) supply comes from another location where the UPS is. The whole DB is on UPS and as you can imagine there is no chance of them switching the main UPS on bypass so the test can be performed.

Similar Threads

  1. Mining Equipment/Supplies Scam
    By Martinco in forum Scam Alert Forum
    Replies: 6
    Last Post: 22-Apr-24, 12:17 PM
  2. [Question] Compliance certificate and multiple supplies
    By christopher john in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 25-Jan-13, 07:57 AM
  3. Fuel supplies fragile
    By Dave A in forum General Business Forum
    Replies: 0
    Last Post: 27-Apr-08, 01:54 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •