    Had this a few times. Often its that there is no proper incoming earth(from the supplier - bad cable joint in the road somewhere or at sub station or a little bit of copper theft) or the earth fault loop impedance is high so even when the is a fault to earth(as Andy says 2 faults) the fault current flowing is so low its not enough to trip the breaker.

    Some dopey electrician come in and uses a multi meter and gets 220v between live and earth and "yes there is earth" but the shocks continue. Yes there is earth, those water pipes go into the ground and you get a kind of earth through the bonding and yes there is 220 between live and "kind of earth". I come in with my nice loop tester and find the external earth fault loop is high(or non existent). Not enough to trip the earth leakage but when the poor customer in question when he/she is soaking wet in a shower the resistance is a little lower and he/she gets a surprises.

    First thing to check. Do i have an incoming earth(test with a proper loop tester not a multimeter). Then find the other fault.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Quote Originally Posted by skatingsparks View Post
    ......Some dopey electrician come in and uses a multi meter and gets 220v between live and earth and "yes there is earth" but the shocks continue.
    Yeah, this is one of my pet hates, incorrect use of test equipment and the user not understanding the characteristics of the tester and what it's actually indicating. The electrician you describe would be the same kinda idiot that can't understand why his digital multimeter shows 95v between a live that's been isolated at the circuit breaker and a neutral or earth.

    Sorry, rant over.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Earthing
    By TECHNICIAN 810 in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 04-Apr-23, 04:53 AM
  2. Another earthing question
    By adrianh in forum Technology Forum
    Replies: 6
    Last Post: 16-Feb-14, 05:03 PM
  3. Earthing and the CoC
    By WallyL in forum General Regulatory Compliance Forum
    Replies: 11
    Last Post: 20-Jan-11, 12:06 AM
  4. Are employees interchangeable parts?
    By duncan drennan in forum Entrepreneurship and Business Management Forum
    Replies: 3
    Last Post: 17-Sep-08, 08:34 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •