Page 2 of 3 FirstFirst 123 LastLast
Results 11 to 20 of 24

Thread: 2 speed motor 3 phase 380 volt motor

  1. #11
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Quote Originally Posted by bergie View Post
    we have been waiting patiently all these years to see andy get stumped.
    TBH It's not that rare, I get stumped quite regularly. I've never worked on a Dahlander Motor installation but I live in hope.

    You can fully enclose a VFD in an enclosure without ventilation but there strict manufacturer recomendations on how much surface area the enclosure must have to allow the heat to be dissipated and it must be of metal construction. The enclosure size is also relative to external ambient temperatures so if it's being used outdoors in a ventilated and shaded area then it should be a sensible size. The last drives we had to fully enclose in a plant room (44 degrees C ambient) the enclosure needed to be 1000 x 1200 x 500mm and mounted on spacers to hold it off the wall in order to fulfil the heat dissipation requirements. We also installed a small tangential blower similar to an air curtain above them just to play it safe.
    _______________________________________________

    _______________________________________________

  2. #12
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    so the enclosure for the drive would be a bit big for a portable pump on a trolley. not to mention the exd enclosure would also cost a fortune.

  3. #13
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by bergie View Post
    so the enclosure for the drive would be a bit big for a portable pump on a trolley. not to mention the exd enclosure would also cost a fortune.
    But Bergie the enclosure along with the VSD would be far cheaper than the R45K you mentioned in one of your posts. Being portable, does this not make the extension a challenge to maintain in a hazardous area?

    If it is variable pumping output you require, then a loop back valve system may be a cheaper solution with a single speed motor.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #14
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    i think the enclosure for the vsd would be too big and impractical. the customer can decide,they have big budgets. their mechanical engineer doesnt have an easy mechanical solution either.

  5. #15
    New Member
    Join Date
    Mar 2014
    Location
    Shenzhen, China
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Please check the drawing. I upload many times. I do not know whether I can upload successfully this time.Click image for larger version. 

Name:	QQ截图20140317210553.jpg 
Views:	595 
Size:	27.3 KB 
ID:	4474

  6. #16
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    looks correct,although i'm not sure why the overload contacts are on the star point

  7. #17
    New Member
    Join Date
    Mar 2014
    Location
    Shenzhen, China
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by bergie View Post
    looks correct,although i'm not sure why the overload contacts are on the star point
    It should be on the star point. It is a 3 phase motor. Each winding powers on independently. If the overload protector is just on one winding, when overload happens, the protector just can cut off one winding power. The other two windings still power on. Then the motor can still run. So the protector must be on the star point, when overload happens, the protector can cut off all the windings power once.

  8. #18
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    an overload relay just switches the contactor off and all windings have no power. the star point of a motor can be connected to neutral,but doesnt need to be

  9. #19
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts
    Hi a quick sketch of how it should be wired up I did the power circuit and the control circuit Two Speed Motor Circuit.pdf

  10. #20
    New Member
    Join Date
    Mar 2014
    Location
    Shenzhen, China
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by bergie View Post
    an overload relay just switches the contactor off and all windings have no power. the star point of a motor can be connected to neutral,but doesnt need to be
    I can not understand what you want. And what is the problem? I think it is ok design like this.

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. single phase motor advice
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 20
    Last Post: 03-Feb-14, 07:10 AM
  2. Motor suppliers
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 14-Mar-13, 10:33 AM
  3. VAT on motor oil
    By J7J in forum Tax Forum
    Replies: 2
    Last Post: 12-Jan-12, 09:46 PM
  4. 3 Phase motor foward/reverse with cam switch
    By superspark in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 05-Dec-11, 10:55 AM
  5. NEW MOTOR INSURANCE OFFER
    By Phil Cooper in forum General Business Forum
    Replies: 5
    Last Post: 29-Nov-10, 01:39 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •