Page 1 of 3 123 LastLast
Results 1 to 10 of 24

Thread: 2 speed motor 3 phase 380 volt motor

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts

    2 speed motor 3 phase 380 volt motor

    i am doing a new installation of a 2 speed motor. 5.5kw/7.5kw
    i think both windings are internally connected star,so i it should be 2 contactors for slow and fast.
    my question is ,should you use 2 overload relays as the current is different in each speed?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Can you give the exact make and model number of the motor? Is it definately wound with two sets of three windings for the two speeds? I'm not sure how this arrangement would work TBH, the rotatonal speed of a 3-phase motor is determined by the number of poles in the windings and I'm not sure if you can have a motor that's wound for example as 4 pole and 6 pole at the same time. Are you sure it's not just a standard wound motor that has the option to be wired in star or delta depending on the application? Without more info I would risk advising on overload protection.
    _______________________________________________

    _______________________________________________

  3. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    OK found it it is called a Dahlander motor
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #4
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Hi Andy,

    There is such a thing as a dual speed induction machine. I just can not recall the name for it. By switching the connections to the windings, the stator changes from a 2 pole to a 4 pole machine.
    Not very common, but is available.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  5. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    It's possible in theory so I've no doubt some lunatic somewhere will be making them but I've never seen one. If it was a 2-pole and 4-pole arrangement within a single stator then you could be looking at 16 winding wires on the connection termination block. Rather you than me connecting and commissioning Bergie
    _______________________________________________

    _______________________________________________

  6. #6
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Hi Andy,

    The Dahlander motor is a a reality, you can order from your local motor supplier.They may not know what you are talking about, but if they are worth their salt they will.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  7. #7
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    i've encountered them a few times ,but fortunately in this application it would be internally connected star. now to find it in EXD . the cheapest i found so far is about R 45000 ex vat for a 5.5kw.
    we have been waiting patiently all these years to see andy get stumped.

  8. #8
    Email problem
    Join Date
    Oct 2012
    Location
    DURBAN
    Posts
    23
    Thanks
    0
    Thanked 3 Times in 2 Posts
    Just a suggestion if its a new installation why not use a VSD

  9. #9
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Quote Originally Posted by bergie View Post
    we have been waiting patiently all these years to see andy get stumped.
    TBH It's not that rare, I get stumped quite regularly. I've never worked on a Dahlander Motor installation but I live in hope.

    You can fully enclose a VFD in an enclosure without ventilation but there strict manufacturer recomendations on how much surface area the enclosure must have to allow the heat to be dissipated and it must be of metal construction. The enclosure size is also relative to external ambient temperatures so if it's being used outdoors in a ventilated and shaded area then it should be a sensible size. The last drives we had to fully enclose in a plant room (44 degrees C ambient) the enclosure needed to be 1000 x 1200 x 500mm and mounted on spacers to hold it off the wall in order to fulfil the heat dissipation requirements. We also installed a small tangential blower similar to an air curtain above them just to play it safe.
    _______________________________________________

    _______________________________________________

  10. #10
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    A VSD would be far cheaper, and just as effective. If the client wishes to have 2 speeds only, and is not keen on a potentiometer, then get 2 potentiometers, which are set for the 2 speeds he requires and use a switch to select the pot for the speed required.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Page 1 of 3 123 LastLast

Similar Threads

  1. single phase motor advice
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 20
    Last Post: 03-Feb-14, 07:10 AM
  2. Motor suppliers
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 14-Mar-13, 10:33 AM
  3. VAT on motor oil
    By J7J in forum Tax Forum
    Replies: 2
    Last Post: 12-Jan-12, 09:46 PM
  4. 3 Phase motor foward/reverse with cam switch
    By superspark in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 05-Dec-11, 10:55 AM
  5. NEW MOTOR INSURANCE OFFER
    By Phil Cooper in forum General Business Forum
    Replies: 5
    Last Post: 29-Nov-10, 01:39 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •