    When I was reading through my SANS 10142 book, I came across a statement which I think does not make sense to me, see bow pic

    Does this means you can install the SSO even in water??

    Click image for larger version. 

Name:	SSO Positioning.jpg 
Views:	2065 
Size:	45.9 KB 
ID:	4421

  2. #2
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    909
    Thanks
    21
    Thanked 127 Times in 96 Posts
    You may, provided it complies with the conditions stipulated. Why would you?

  3. #3
    Full Member
    Join Date
    Feb 2014
    Location
    Fish Hoek
    Posts
    55
    Thanks
    6
    Thanked 3 Times in 3 Posts
    You can mount it over the bath with a small shelf for the two bar electric heater if its connected to an earth leakage unit.
    Err no I wouldn't do this, and yes I have been asked to do it.
    Apparently there is nothing that cannot happen today.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Quote Originally Posted by Smut View Post
    Does this means you can install the SSO even in water??
    I'd prefer to look at the regs as being the minimum required standards, there will always be scenarios that aren't specifically mentioned or covered which require the competant electrician to make a decision based on his knowledge, experience and common sense. The question I usually ask myself in these cases is if the worst ever came to the worst how comfortable would I be to stand in a courtroom and defend my actions or decision?
    _______________________________________________

    _______________________________________________

  5. Thanks given for this post:

    Leecatt (03-Mar-14)

  6. #5
    New Member
    Join Date
    Aug 2012
    Location
    Cape Town
    Posts
    4
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Quote Originally Posted by Slow Blow View Post
    You can mount it over the bath with a small shelf for the two bar electric heater if its connected to an earth leakage unit.
    Err no I wouldn't do this, and yes I have been asked to do it.
    Hi Slow Blow, I beg to differ. Over the bath would be zone 1 up to 2.5m high from the water so no plugs allowed, zone 2 within 600mm from the bath edge also no plug unless 50va safety supply like a shaver. Zone 3 outside 600mm would be the closest you can mount a plug to a bath or shower.
    So to answer the initial question, no you can't mount a socket outlet in water, first check the zone rules for baths, showers, pools, fountains etc.

  7. Thanks given for this post:

    Leecatt (03-Mar-14)

  8. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    "Does this means you can install the SSO even in water??"


    6.15.6.2 answers your question...The insulation resistance must not be affected. So you might say but I can seal the box, you would be correct, but you would never be able to use the socket outlet.

  9. #7
    New Member
    Join Date
    Aug 2012
    Location
    Cape Town
    Posts
    4
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Quote Originally Posted by ians View Post
    "Does this means you can install the SSO even in water??"


    6.15.6.2 answers your question...The insulation resistance must not be affected. So you might say but I can seal the box, you would be correct, but you would never be able to use the socket outlet.
    Hi Ians, 6.15.6.2 pertains specifically to a recessed floor plug and has nothing to do with mounting a plug in or near water.
    The same can't be said for other parts of sans 10142 but when it comes to socket outlets and water then it is very clear as to what you are allowed or not allowed to do.

  10. #8
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    909
    Thanks
    21
    Thanked 127 Times in 96 Posts
    but you may install a socket outlet underneath the bath, in which case it is "under" the water and it would be totally legit
    The space below a bath is not considered to be "in the bathroom".

  11. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Smut View Post
    When I was reading through my SANS 10142 book, I came across a statement which I think does not make sense to me, see bow pic

    Does this means you can install the SSO even in water??

    Click image for larger version. 

Name:	SSO Positioning.jpg 
Views:	2065 
Size:	45.9 KB 
ID:	4421
    I was responding to this question with this attachment. Common sense would tell me that the insulation resistance of "any socket outlet" regardless of its location, bathroom, kitchen, outdoors, etc, would be affected if installed "in water".

    This question makes me think of the picture doing the rounds, where there is a multi plug floating on a slop in a pool. Nothing illegal about it, because for one it doesn't form part of the electrical installation as it is cable plugged into a socket outlet. There would be people stupid enough to actually do it. So long as the electrician who installed and connected the socket outlet which is fed from is done according to regulations, there would be no recourse on him.

    However in saying that, I have seen on more than one occasion on work sites where it is pouring down with rain and plugs are exposed in puddles, which is just as risky.

    This is why there have to be at least a basic set of rules.

  12. #10
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    I think what is forgotten at times when it comes to complying with the standard, is that you have to comply with the whole standard.

    The question one has to ask is not - "does this comply with this part of the standard", but "does it transgress any part of the standard?"

    In relation to socket outlets and water, it's highly likely that parts of section 7 Special installations or locations will also be applicable, not just S 16.6.

  13. Thanks given for this post:

    ians (03-Mar-14)

Page 1 of 2 12 LastLast

Similar Threads

  1. unknown socket outlet
    By pipewood in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 09-Nov-12, 06:38 PM
  2. Socket outlet in bathroom
    By mlpotgieter in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 23-Oct-11, 12:10 AM
  3. sabs approved socket outlet
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 15-Sep-10, 12:52 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •