    Hi All

    Need some help please.
    I have a large customer that has had most of his earthing stolen.
    The building has various 11kv substations that feed LV rooms that feed sub DB’s that feed consumer DB’s
    The layout out does not allow for complete new copper earthing and neither does the budget. We have installed various earth bonding straps and used all the armouring strands that we can get our hands on. We have managed to get the Ze of the sub DBs down to 0.11 Ohms. (Main breaker off and new earth strap disconnected)
    Now if we follow SANS
    I have a Main breaker of 1250Amps
    So calculate Ze = 240V/2(1250) = 0.096 Ohms.
    I have tried many things including new copper earthing and I can NOT get it below the 0.1 Ohm mark.

    Many thanks
    Neal

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    It wouldn't be chrome international by any chance?

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,945
    Thanks
    582
    Thanked 938 Times in 759 Posts
    Can you maybe attach a drawing of your system layout? Is the LV main earth busbar bonded back to the main substation earth (are the HV and LV earths bonded)? What is the arrangement on the LV side (TN-S TN-C-S TN-C)?

    Immediately I'm sceptical about achieving a sub0.1 ohm Ze using aluminum, what CSA have you specified and how did you come up with the requirement of 0.096ohms? Also how are you measuring your present Ze of 0.11ohms, what instrument and what proceedure are you using?
    Last edited by AndyD; 19-Jun-13 at 01:27 AM.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. [Question] Loop Impedance
    By C-Cam in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 20-Jan-21, 03:00 PM
  2. Earth loop impedance testing
    By ians in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 24-Jan-19, 09:34 AM
  3. Earth loop impedance and prospective short circuit (PSC)
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 21-Jan-16, 04:10 PM
  4. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  5. Google Earth
    By Faan in forum General Business Forum
    Replies: 0
    Last Post: 30-Jul-08, 08:52 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •