Thread: Earth Loop (Can it be achieved?)

Threaded View

Previous Post Previous Post   Next Post Next Post
  1. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,945
    Thanks
    582
    Thanked 938 Times in 759 Posts
    Can you maybe attach a drawing of your system layout? Is the LV main earth busbar bonded back to the main substation earth (are the HV and LV earths bonded)? What is the arrangement on the LV side (TN-S TN-C-S TN-C)?

    Immediately I'm sceptical about achieving a sub0.1 ohm Ze using aluminum, what CSA have you specified and how did you come up with the requirement of 0.096ohms? Also how are you measuring your present Ze of 0.11ohms, what instrument and what proceedure are you using?
    Last edited by AndyD; 19-Jun-13 at 01:27 AM.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. [Question] Loop Impedance
    By C-Cam in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 20-Jan-21, 03:00 PM
  2. Earth loop impedance testing
    By ians in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 24-Jan-19, 09:34 AM
  3. Earth loop impedance and prospective short circuit (PSC)
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 21-Jan-16, 04:10 PM
  4. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  5. Google Earth
    By Faan in forum General Business Forum
    Replies: 0
    Last Post: 30-Jul-08, 08:52 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •