Is an earth leakage faulty if it trips before or after the mA rating stipulated on the earth leakage?
Is an earth leakage faulty if it trips before or after the mA rating stipulated on the earth leakage?
I had this discussion with my electrician this morning. In my opinion it is definitely faulty if it trips after, as anything over 100 milliamps becomes lethal. It can also be faulty if it is too sensitive and trips around the 20 milliamps range, however not lethal, I think, it trips too quick and needs to be replaced. Any electricians out there that can shed some more light on this?
i think in sans it says 20 -30ma is acceptable. i need to go back and check.
Yes it is acceptable but would if the manufacturer standards stipulates 20mA on it, it must trip on that rating. But what if it doesn't. Even if it's a new earth leakage. Where is the fault?
Is it tripping before or after?
The earth leakage is faulty if it doesn't trip after 30 Ma or if it trips when all the wiring is disconnected.
I had this problem last week, earth leakage and random tripping.
I tested the unit with no load connected and found it was very sensitive and tripped at 21 Milli-amps.
I found another unit that trips at 25 Milli-amps and the problem has gone now.
By the way the acceptable range for any earth leakage unit is between 50% and 100% of its rating as indicated on the unit.
For a modern home that would be between 15 and 30 Milli-amps
To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.
A common problem with random tripping, surge protection plug tops, they break down under load and cause random tripping.
Another common problem, cut insulation on surfix, I have found insulation cut where the electrician strips the cable and doesn't use tape, it gets moisture in the cut and cause nuisance tripping.
In fact there are so many, a good electrician will identify the problem and repair it and others will find other means to overcome the problem, bypassing a stove is one of the common remedies.
See
8.7.12 Operation of earth leakage units
To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.
This house had various areas from where there were earth leakages. Some where electronic equipment, slight leakage at geysers and borehole pumps and various flourescent lights. Too many to mention here. Eventually it exceeded the 21 milliamps the earth leakage worked at or perhaps the unit had become more sensitive over time, and the only alternative was to raise the threshold of the earth leakage unit.
To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.