    A common problem with random tripping, surge protection plug tops, they break down under load and cause random tripping.

    Another common problem, cut insulation on surfix, I have found insulation cut where the electrician strips the cable and doesn't use tape, it gets moisture in the cut and cause nuisance tripping.

    In fact there are so many, a good electrician will identify the problem and repair it and others will find other means to overcome the problem, bypassing a stove is one of the common remedies.

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    404
    Thanks
    25
    Thanked 47 Times in 43 Posts
    This house had various areas from where there were earth leakages. Some where electronic equipment, slight leakage at geysers and borehole pumps and various flourescent lights. Too many to mention here. Eventually it exceeded the 21 milliamps the earth leakage worked at or perhaps the unit had become more sensitive over time, and the only alternative was to raise the threshold of the earth leakage unit.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. #3
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    404
    Thanks
    25
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by ians View Post
    A common problem with random tripping, surge protection plug tops, they break down under load and cause random tripping.

    Another common problem, cut insulation on surfix, I have found insulation cut where the electrician strips the cable and doesn't use tape, it gets moisture in the cut and cause nuisance tripping.

    In fact there are so many, a good electrician will identify the problem and repair it and others will find other means to overcome the problem, bypassing a stove is one of the common remedies.
    This house had various areas from where there were earth leakages. Some where electronic equipment, slight leakage at geysers and borehole pumps and various flourescent lights. Too many to mention here. Eventually it exceeded the 21 milliamps the earth leakage worked at or perhaps the unit had become more sensitive over time, and the only alternative was to raise the threshold of the earth leakage unit.

    It is incorrect to remove a stove from the earth leakage protected circuit unless it is connected via a "stove coupler"
    See 6.16.3.3 Stove connection.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. Earth leakage trips at night??
    By Jongseun in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 18-Jun-12, 10:47 PM
  4. Random earth leakage problem
    By BillH in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 23-Jan-12, 09:37 PM
  5. CBI earth leakage units
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Oct-09, 12:44 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •