    Quote Originally Posted by MullerR View Post
    Yes that im aware of. The measured value must not be more than the calculated value, as the calculated value is the upper limit threshold as you mentioned. My question now, when i calculate the value of the pscc, must i use the earth loop value calculated (1.90ohm) or the measured value (0.36ohm) to get the pscc? Because when i use the measured value of 0.36ohm, I get 633A which is closer to the pscc measurement of 674A.
    You'd use the measured value. The objective of establishing the actual PSCC is to ensure the protection equipment is adequately rated to handle a short-circuit situation for that particular installation, so you need to be using the actual values of the environment.

    As an aside, when you have a moment read Section 8.5 of SANS 10142-1 to get where I'm coming from on what the term "calculated PSCC" means.

  2. Thanks given for this post:

    MullerR (21-Jan-16)

  3. #12
    Full Member MullerR's Avatar
    Join Date
    Jan 2016
    Location
    Lady Grey
    Posts
    44
    Thanks
    3
    Thanked 6 Times in 5 Posts
    Now i'm getting closer to everything. Still a bit rusted, but between the books and guys like you who can answer me when I ask something, I feel more comfortable now.

    Thank you Dave and Andy

  4. Thanks given for this post:

    ACEsterhuizen (27-Jan-16)

Page 2 of 2 FirstFirst 12

Similar Threads

  1. [Question] Loop Impedance
    By C-Cam in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 20-Jan-21, 03:00 PM
  2. buzzzing circuit breaker
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 08-Mar-11, 10:47 AM
  3. why do lights blow regularly on one circuit & very seldom on another, both supplied f
    By harveya in forum Electrical Contracting Industry Forum
    Replies: 24
    Last Post: 20-Nov-10, 10:38 PM
  4. Circuit breakers
    By adrianh in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 25-May-10, 12:37 AM
  5. Software program for electrical circuit diagrams
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 04-Jan-09, 02:10 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •