    Here is the scenario: you climb in the roof and it is wired in pvc cleated wiring running into metal downpipes.
    The older installation has earth wires attached to the exposed portion of the metal downpipes, in the roof.
    On the older installation there are no earth wires running down into the pipes, to the light switches or plugs.

    There have been some additional plugs and lights and they have been wired using pvc pipe and pvc wires which are tapped of the older installation.
    The new additions have all got the required earthing which is also tapped of the older installation


    SANS says "If an existing
    installation is extended or altered, such extension or alteration has to comply
    with the provisions of this part of SANS 10142 that were applicable at the
    time of the erection of the extension or alteration
    ."

    I take this to mean that only the new portion of the circuit has to comply with the latest regs.

    In a recent statement in the media it was said that "changing a plug socket or light switch does not constitute an alteration therefore you must not upgrade the older installation when changing a plug socket or light switch."

    In my given example if you change a plugsocket or light switch then you must upgrade the effected circuit to the latest regs because the new sockets and light switches have different requirements to the older ones. For example the new plugs need an earth wire connection, and connecting a wire from the earthing terminal to a screw on the metal housing is "using the pipework as an earth continuity path" which is no longer legal.

    Another thing is, by installing the new plugs an earth leakage now has to be added to the circuit. After that is done EVERY plug has to have an earth wire as required by the earth leakage.

    Comments?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts

    aGAIN

    Quote Originally Posted by Leecatt View Post
    Here is the scenario: you climb in the roof and it is wired in pvc cleated wiring running into metal downpipes.
    The older installation has earth wires attached to the exposed portion of the metal downpipes, in the roof.
    On the older installation there are no earth wires running down into the pipes, to the light switches or plugs.

    There have been some additional plugs and lights and they have been wired using pvc pipe and pvc wires which are tapped of the older installation.
    The new additions have all got the required earthing which is also tapped of the older installation


    SANS says "If an existing
    installation is extended or altered, such extension or alteration has to comply
    with the provisions of this part of SANS 10142 that were applicable at the
    time of the erection of the extension or alteration
    ."

    I take this to mean that only the new portion of the circuit has to comply with the latest regs.

    In a recent statement in the media it was said that "changing a plug socket or light switch does not constitute an alteration therefore you must not upgrade the older installation when changing a plug socket or light switch."

    In my given example if you change a plugsocket or light switch then you must upgrade the effected circuit to the latest regs because the new sockets and light switches have different requirements to the older ones. For example the new plugs need an earth wire connection, and connecting a wire from the earthing terminal to a screw on the metal housing is "using the pipework as an earth continuity path" which is no longer legal.

    Another thing is, by installing the new plugs an earth leakage now has to be added to the circuit. After that is done EVERY plug has to have an earth wire as required by the earth leakage.

    Comments?
    does anyone have an opinion on this, i am trying to get a debate around this to see if I am wrong
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,688
    Thanks
    3,315
    Thanked 2,682 Times in 2,262 Posts
    Blog Entries
    12
    My thought is if you're replacing a plug point on an old installation, there usually is an existing earthing point to use.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,934
    Thanks
    579
    Thanked 936 Times in 757 Posts
    I didn't take a stab at this cause I didn't understand the question fully.

    Which parts of the socket circuit are the original 2-wires in steel conduit and which parts are PVC conduit with housewire or FT&E?

    Am I along the right lines with this setup?

    Click image for larger version. 

Name:	Dwg1.jpg 
Views:	462 
Size:	22.2 KB 
ID:	2680
    _______________________________________________

    _______________________________________________

  5. #5
    Bronze Member dfsa's Avatar
    Join Date
    Jun 2012
    Location
    SA
    Posts
    166
    Thanks
    8
    Thanked 31 Times in 24 Posts
    You have come across an original installation before earth leakage time. At the time it was purely a 2 wire system and the actual earth was used for neutral. That was also at the time where open wires was used in the roof. You should find that the old section have the wires a couple centimeters apart and fixed onto insulators. Around 30 Years ago the law changed where plugs and appliances needed to be run through an eart leakage, to prevent people from getting shocked if there are a leakage from any metal surface.

    When the extensions was done on the installation you found, the original part of the installation was supposed to be upgraded to all run via the earth leakage and extra earthing to all points was supposed to have been installed.

    If you replace an older plug socket ( You will find it is actually bakelite) to a new one, you need to pull the needed earth from the socket to the nearest earth point. Even with today's new plastic socket covers, you still need the earthing, because people might still plug a 3 wire appliance into the socket and then will need the earthing for leakage protection.

  6. #6
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by AndyD View Post
    I didn't take a stab at this cause I didn't understand the question fully.

    Which parts of the socket circuit are the original 2-wires in steel conduit and which parts are PVC conduit with housewire or FT&E?

    Am I along the right lines with this setup?

    Click image for larger version. 

Name:	Dwg1.jpg 
Views:	462 
Size:	22.2 KB 
ID:	2680
    Almost. there are no cables involved. This is an old installation. The original socket circuit was wired as such: two pvc wires, red and black, exiting the Db board conjute metal piping, mounted upon cleats and running through the roof. Every so often there is a joint, with another 2 wires, and those 2 wires run away from the cleated wires and into a metal conjute down to a plug. The lighting circuit is similar. All the metal conjute pipes are bonded at the exposed part in the roof, to a earth wire and then usually to the water pipes. The earth wire does not travel down the pipe with the red and black wire.
    The question is, when the socket outlet is replaced, does there have to be an earth wire delivered down the conjute pipe to the new socket outlet (i support this theory) or are you allowed to drill a screw into the metal box and attach a wire from the plug socket to the screw. (I do not support this theory)
    Disregard the extensions for now that was actually for another question
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  7. #7
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,934
    Thanks
    579
    Thanked 936 Times in 757 Posts
    Quote Originally Posted by dfsa View Post
    You have come across an original installation before earth leakage time. At the time it was purely a 2 wire system and the actual earth was used for neutral.
    This sounds like a TN-C system. I've never seen one . An earth leakage breaker (RCD) is unlikely to operate effectively on this system. Single pole disconnects only should be used. I would consider any TN-C system as hazardous and would rewire as TN-C-S and PME the installation.
    _______________________________________________

    _______________________________________________

  8. #8
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    ir depends on who is doing the job...if a handy man is doing it...just take off and replace...if an "electrician" is doing the job...he would replace the plug and put a screw or pop rivet into the steel frame...then carry out a loop impedance test or an earth continuity test...(i would prefer the loop impedance test)...if within the required limits...it is ok...if not then you need to get and earth from a reliable source...back to the db...bonding strap around the pipe in the roof...geyser earth etc etc.

  9. Thanks given for this post:

    Dave A (04-Jul-12)

  10. #9
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by murdock View Post
    ir depends on who is doing the job...if a handy man is doing it...just take off and replace...if an "electrician" is doing the job...he would replace the plug and put a screw or pop rivet into the steel frame...then carry out a loop impedance test or an earth continuity test...(i would prefer the loop impedance test)...if within the required limits...it is ok...if not then you need to get and earth from a reliable source...back to the db...bonding strap around the pipe in the roof...geyser earth etc etc.
    In my opinion, putting a screw or pop rivet into the steel frame would constitute a violation of 6.12.1.3 'A wireway shall not be used as an earth continuity conductor'.
    What do you think?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  11. #10
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,934
    Thanks
    579
    Thanked 936 Times in 757 Posts
    Depends if you're using the actual wireway as the earth or you're just earth bonding the wireway as an extraneous item. In my sketch above the backbox and steel conduit in the wall are bonded, they're not used to actually carry the earth.
    _______________________________________________

    _______________________________________________

Page 1 of 2 12 LastLast

Similar Threads

  1. Connecting backup generators to existing electrical installation
    By Kevin Stubbs in forum Electrical Load Shedding Forum
    Replies: 35
    Last Post: 20-Jan-16, 07:28 PM
  2. building alteration requirements
    By murdock in forum General Chat Forum
    Replies: 1
    Last Post: 21-Oct-11, 09:42 PM
  3. [Question] Existing vs New/altered /temp installation?
    By siphom_3 in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 21-Jun-11, 03:44 PM
  4. [Article] Funding for existing businesses
    By QUINN in forum Business Finance Forum
    Replies: 0
    Last Post: 11-May-09, 05:22 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •