Kleva was suggesting outside Zone 3 which would be 3.6m from shower. I would install a diffuser and some flexible duct in the shower itself and fit an inline fan in the roof space somewhere outside Zone 1 &2 with a 2 or 3-pole isolater depending on the type of fan and also RCD protection and a discharge louvre through the outside wall. This would depend what is above your bathroom ceiling hence my earlier question.
Code:
6.14.2.3 In a room that contains a fixed bath or shower cubicle,
luminaires shall be totally enclosed or the parts of the lamp holder within
a distance of 2,5 m from the bath or the shower cubicle shall be
constructed of or shrouded in insulating material.
6.14.3 Suspended luminaires
6.14.3.1 The luminaire and pendant shall not rotate more than one
complete revolution to prevent damage to the conductors.
6.14.3.2 A luminaire pendant which is longer than 600 mm and not
suitably stayed, shall have a flexible joint.
NOTE A rigid pendant is deemed to be suitably stayed if the lower end of the
pendant cannot move horizontally by more than 25 mm per 500 mm (or part of
500 mm) length of the pendant.
6.14.3.3 A suspended luminaire shall be out of arm's reach from the floor
if the luminaire is installed in a
a) washroom,
b) change room,
c) laundry,
d) cupboard or other enclosure, or
e) position exposed to wind and the weather.
Code:
7.1.2.1 Zone 0
Zone 0 is the interior of the bathtub or shower basin (the container).
7.1.2.2 Zone 1
Zone 1 is limited by
a) the vertical plane circumscribing the outer edge or 0,20 m from the
inner edge (where the ledge is too wide) of the bathtub, shower basin,
or for a shower without a basin, by the vertical plane 0,60 m from the
shower rose, and
b) the horizontal plane 2,5 m above the bathtub or shower floor.
7.1.2.3 Zone 2
Zone 2 is limited by
a) the volume external to zone 1 and the parallel vertical plane 0,60 m
external to zone 1, and
b) the floor and the horizontal plane 2,25 m above the floor.
7.1.2.4 Zone 3
Zone 3 is limited by
a) the vertical plane external to zone 2 and the parallel vertical plane
2,40 m external to zone 2, and
b) the floor and the horizontal plane 2,25 m above the floor.
Code:
7.1.4.1 Degrees of protection
Electrical equipment shall have at least the following degrees of
protection against ingress of water:
in zone 0 : IPX7;
in zone 1 : IPX5;
in zone 2 : IPX4;
in zone 3 : IP21; and
outside zone 3 in the same room : IP21, except for a distribution board :
IPX5
7.1.4.2 Wiring systems
7.1.4.2.1 In zones 0, 1 and 2, wiring systems shall be limited to those
necessary for the supply of appliances situated in these zones.
7.1.4.2.2 Junction boxes are not permitted in zones 0, 1 and 2.
7.1.4.3 Switchgear and controlgear
7.1.4.3.1 In zones 0, 1 and 2, no switchgear and accessories shall be
installed except that emergency push buttons, which operate at a safety
This eStandard is exclusively for use on one standalone PC. To access it from a file server/Intranet constitutes a violation
of SABS copyright rules. Note that only one printout of the standard may be made.
SANS 10142-1:2003
Edition 1.1
(As amended 2003 and 2005)
extra low voltage at nominal voltage not exceeding 12 V, are permitted in
zones 1 and 2.
7.1.4.3.2 Insulating cords of cord-operated switches are permitted in
zones 1 and 2, provided that the cord-operated switch complies with the
requirements for switches (see table 4.2).
7.1.4.3.3 In zone 3, socket-outlets are permitted only if they are
a) supplied individually by an isolating transformer that complies with
SANS 61558-2-6/IEC 61558-2-6 (SABS IEC 61558-2-6), or
b) supplied by safety extra low voltage (SELV) (see 5.7), or
c) protected by an earth leakage protection device with a rated earth
leakage tripping current (rated residual current) IΔn not exceeding
30 mA. Amdt 3
7.1.4.3.4 Any switches and socket-outlets shall be at a distance of at
least 0,60 m from the door opening of the prefabricated shower cabinet