heineman/cbi have both the heineman unit and the new clip system...or you can get the one for the din rail mount type breakers from AC/DC...dont forge tto print and laminate a dange rdo not switch on label with your contact details
Dave A (20-Feb-12), SparkyScott (19-Feb-12)
Hi guys
It is compulsory to have an isolator installed within arm's reach of the gate motor, so that the electrical power can be cut should an emergency situation arise. It is recommended that a 5A thermal breaker with all-pole circuit break is used. Page 14 of this installation manual shows the position of the isolator.
I hope this helps :-)
Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services
Sure, it is in the SANS10142-1 manual, section 6.9.3 - Disconnecting devices for equipment Amdt 3
6.9.3.1 An appliance or equipment that is not supplied from a socket-outlet, including equipment automatically or remote controlled, shall be capable of being disconnected from the supply by an easily accessible switch-disconnector. The disconnector shall be mounted (if not specified elsewhere in this part of SANS 10142, but excluding luminaire circuits) (see also 6.16.1.4) Amdt 1
a) within arm's reach from the terminals of the appliance, or
b) in a distribution board, if the device is capable of being locked in the open position
I see we have come full circle. This was the starting point of post 1, but with a totally different interpretation.
Please note the highlighted bits above which are pretty important to the correct interpretation...
Just in the section you've quoted we've already got a couple of options other than the isolator within arms reach:
- The appliance is supplied from a socket-outlet - you don't need an isolator within arms reach of the terminals of the appliance (unless specified elsewhere)
- There is a lockable switch disconnector device in the distribution board - you don't need an isolator within arms reach (unless specified elsewhere)
The "if not specified elsewhere" bit is touched on in post 9. Section 6.16.5.1 is all about motor protection and control - and 6.16.5.1.5 provides four options, only one of which is a disconnector "mounted on or next to the motor".
Last edited by Dave A; 20-Feb-12 at 04:25 PM. Reason: typo
Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services
Kevin, there's no harm in that. It's a great way to do it
It's when people start stating it's "compulsory" - i.e. the only way to do it that the problems start. People start believing it, then sparkies who issue COC's on an installation that is up to code, but deals with this issue a different way, start copping flack because folk have been misinformed.
It's unnecessary aggravation and I'd prefer to nip it in the bud before the disease spreads.
The big question that still remains, given Andy's lockable plug-top device option, is whether any plug-top can therefor be considered a lockable disconnector device?
For the time being I've advised my sparkies not to rely on the idea when examining installations... for no better reason than it would make the line of site to plug point option redundant (and that would still have to be complied with when it comes to motors on plug-tops anyway).
It's for things like these that a practice note from the regulatory authority would be really useful.
Last edited by Dave A; 20-Feb-12 at 08:33 PM. Reason: update - clarification
Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services
I think you've hit the nail on the head. From a real world point of view a 16A 3-pin plug (or any other plug) is a device that would easily fulfil the definition of being a safe lock-out device. Sure you need a 'tool' to do it but that's no different than an MCB or MCCB where many brands require their own proprietary toggle clip. I'm guessing that the legislation was written by persons who weren't aware of suitable devices being on the market and I have to say they wouldn't be alone, I'm yet to see anyone else making use of these devices.
I agree there's no 'harm' in making the plug point within a meter but it's certainly an unnecessary inconvenience in many cases and possibly extra expense. If I was involved in domestic electrical or access systems work it would annoy the hell out of me but as I'm not I refuse to get stressed about it. The ball's in you're court Dave I wish you luck and Godspeed. Let us know how you get on with the appropriate authorities.
_______________________________________________
_______________________________________________
I get called out quite a lot because someone might be selling a house and they cannot get a coc, because the motor was installed a couple of years ago and does not have a plugpoint within one metre of the gate therefore they cannot get a coc. So this comes from a lot of different sparkies who insist on this to issue the coc.