Eskom Fact Sheet On Generators.

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • AndyD
    Diamond Member

    • Jan 2010
    • 4946

    #1

    Eskom Fact Sheet On Generators.

    Eskom generates electricity by transforming inputs from the natural environment – coal, water, wind, nuclear and liquid fuels. Together with power generated by independent power producers (IPPs) and imports from neighbouring countries, the electricity is supplied to a wide range of customers, thereby supporting economic growth and improving the quality of life in South Africa and the region.


    Eskom have released a fact sheet on selecting and installing household generators. I was initially quite excited because I though maybe they'd highlight some of the problems with camping and site type generators being totally inappropriate for domestic back-up use.....but alas no.

    My suspicions were raised when I saw the reference to '12 gauge ground wire' in question 10. After some elementary Googling I see they've mostly plagiarized a Popular Mechanics article that was published in June 2011. At the bottom I see they've cunningly stated it was compiled by Eskom Corporate Affairs February 2015 as opposed to written so I guess they're not even trying to hide the fact it's not their handiwork. I hope they're paying royalties!!!
    Last edited by AndyD; 26-Jul-15, 04:56 PM.
    _______________________________________________

    _______________________________________________
  • AndyD
    Diamond Member

    • Jan 2010
    • 4946

    #2
    A standby generator is permanently installed apparatus, much like a compressor for a central air-conditioning system
    That statement hardly helps clarify the purpose of a standby generator for the man on the street.

    As an alternative, the manual may ask you to run a ground wire from the generator's grounding terminal to the ground bus inside the house's service panel. As long as you follow the instructions provided in the manual, the generator will be safely grounded.
    Hmmm, so it's okay for everyone to remove the covers from their DB and connect earth wiring. Also no mention that with newer installations there should be an earth bar somewhere on the premises that's accessible and is specifically for this type of connection. Also a heavy implication that manufacturers instructions should be followed regardless of what SANS 10142 has to say.
    _______________________________________________

    _______________________________________________

    Comment

    • chris.brits@webmail.co.za
      Email problem
      • Jan 2019
      • 8

      #3
      Hi Andy,
      I don't know if this is the right place but if I may, do I need to earth a 7kW home supply generator with a earth rod. Just want to make sure the installtion is safe.
      Regards Chris

      Comment

      • GCE
        Platinum Member

        • Jun 2017
        • 1473

        #4
        Originally posted by chris.brits@webmail.co.za
        Hi Andy,
        I don't know if this is the right place but if I may, do I need to earth a 7kW home supply generator with a earth rod. Just want to make sure the installtion is safe.
        Regards Chris
        You would need to install an earth spike along with indictor lights etc at the DB
        The neutral will also need to be earthed but only when running on generator which can be done with a change over switch , switching neutral as well
        If the genset is VOV it cannot be used and if you complete the installation correctly and the client then hooks up a VOV he will more than likely damage the generator
        Pasted a couple of the regs below


        7.12.2.7 A 230 V generator with a V-O-V earth connection (centre tap on
        winding which is earthed), shall not be connected to a fixed electrical
        installation.
        NOTE Such a generator may be used as a free-standing unit to provide power to
        specific appliances.


        7.12.3.1 Neutral bar earthing
        7.12.3.1.1 Protection in accordance with the requirements of 6.7 shall be
        provided for the electrical installation in such a manner as to ensure correct
        operation of the protection devices, irrespective of the source of supply or
        combination of sources of supply. Operation of the protection devices shall
        not rely upon the connection to the earthed point of the main supply when the
        generator is operated as a switched alternative to the main supply.
        Where there is no existing earth electrode installed in the electrical installation,
        a suitable earth electrode may be installed in accordance with SANS 10199.
        When installed, the electrode shall be bonded to the consumer's earth terminal
        and to the earthing point on the alternate supply by a conductor of at least half
        the cross-section of that of the phase conductor, but not less than 6 mm2
        copper, or equivalent. This also applies to a single-phase supply (see
        also 5.2.3.1).

        7.12.3.1.3 Where alternative supplies are installed remotely from the
        installation, or from one another, and where it is not possible to make use of
        a single neutral bar or neutral conductor which is earthed, the neutral of each
        unit shall be earthed at the unit and these points shall be bonded to the
        consumer's earth terminal (see 6.12.4). The supply from each unit which
        supplies the installation or part of the installation, shall be switched by means
        of a switch that breaks all live conductors operating substantially together (see
        figures P.2 and P.4), to disconnect the earthed neutral point from the
        installation neutral when the alternative supply is not connected (see also
        6.1.6).

        Comment

        • chris.brits@webmail.co.za
          Email problem
          • Jan 2019
          • 8

          #5
          Morning Andy,
          Thankyou for the information. I am new to this so just one more question.
          The generarator is a normal "domestic: gen and currently it is connected to the circuit via a socket outlet. The client just want to make the connection more 'permanent".
          If all this is required he then might aswell carry on to use the socket outlet as the installtion of the change over switch is quite expensive.
          Thanks
          Chris

          Comment

          • GCE
            Platinum Member

            • Jun 2017
            • 1473

            #6
            When you say socket outlet , I presume he is back feeding with 2 plug tops - This is illegal and dangerous and could nullify any insurance claims if there is a fire or damage to equipment

            You have to have a change over switch to prevent feeding back into the supply .If you rely on somebody else to turn the mains off before starting the genset you run the risk of killing a worker on the lines and being charged with manslaughter or the very least disability towards the worker.
            The regulations SANS10142-1 , OHSA and Municipal bylaws are all clear in this regard , all 3 phases and neutral shall be disconnected before an alternative supply is connected.

            7.12.2.5 Where an alternative supply is provided to an installation or part of
            an installation as a switched alternative to the main supply, the change-over
            switching device shall disconnect the main supply before the alternative
            supply is switched in. The change-over switching device shall be interlocked
            in such a way that the main supply and the alternative supply cannot be
            connected to the installation or part of the installation at the same time
            .


            It has happened and documented in court papers ( http://www.saflii.org/za/cases/ZAECGHC/2011/37.html ) .

            At the end the worker was awarded a huge disability pension by the courts

            Advise your client that it is dangerous and illegal , make sure it is in writing so that you never end up standing next to him in court.

            Comment

            • ians
              Diamond Member

              • Apr 2010
              • 3943

              #7
              And that was as far back as 2011 ... and people still do it
              Comments are based on opinion...not always facts....that's why people use an alias.

              Comment

              • adrianh
                Diamond Member

                • Mar 2010
                • 6328

                #8
                Originally posted by chris.brits@webmail.co.za
                If all this is required he then might aswell carry on to use the socket outlet as the installtion of the change over switch is quite expensive.
                Thanks
                Chris
                Scary stuff....

                .....This is why one RATHER pay a Reputable professional to do a job....
                Last edited by adrianh; 12-Nov-21, 02:34 PM.

                Comment

                • Justloadit
                  Diamond Member

                  • Nov 2010
                  • 3518

                  #9
                  Originally posted by adrianh
                  Scary stuff....

                  .....This is why one RATHER pay a Reputable professional to do a job....
                  That's not the African way.
                  A number of expats are returning because they say it is too regulated out there
                  Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                  Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                  Comment

                  • adrianh
                    Diamond Member

                    • Mar 2010
                    • 6328

                    #10
                    Originally posted by Justloadit
                    That's not the African way.
                    A number of expats are returning because they say it is too regulated out there
                    My sister lives in Sydney and often speak about the differences in driving styles - In SA you can drive like a TWAT 24/7 and if you happen to get a fine you just don't pay it and nothing happens - ...doesn't work that way in OZ.

                    If you think you are just going to start your own little business in NZ you are making a huge mistake - They are very very protective of their own "native" industries

                    As you said - people tend to forget that SA is cowboy country - here we do as we please - Other countries don't allow such nonsense.

                    Comment

                    • chris.brits@webmail.co.za
                      Email problem
                      • Jan 2019
                      • 8

                      #11
                      Thank you everybody. That iswhy I asked the question. There are a lot of people in my area doing just that. I will stay clear of trouble. Regards