    Light switch.

    Presently there are 3 rows of 5ft fluorescents each on their own 15A breaker. The lights are turned off at the circuit breakers in the DB.

    They now want a 3 lever switch installed at the front door.

    My question is. May one bring 3 lives into a 3 lever switch or must one install 3 seperate single lever switches, each with it's own live ?
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #2
    We fit a din mount contactor in the DB and run the switch wire (relay coil) to a surface 4x2 box with a single lever switch.


    Originally posted by Derlyn
    Presently there are 3 rows of 5ft fluorescents each on their own 15A breaker. The lights are turned off at the circuit breakers in the DB.

    They now want a 3 lever switch installed at the front door.

    My question is. May one bring 3 lives into a 3 lever switch or must one install 3 seperate single lever switches, each with it's own live ?
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

    Comment

    • Isetech
      Platinum Member

      • Mar 2022
      • 2274

      #3
      If you want 3 switches, just fit 3 din contactors in the DB and run 4 wires to the 3 lever switch, that way you only have 1 phase controlling the lights.
      Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #4
        Good idea for the contractors.

        As far as I know you can have 3 power supplies to the switch however they have to be the same phase.. you may be able to do different phases but warming stickers need to be there that there is 400volts. However need to check the book as even that may be a no go.

        The safest route I reckon is contactors. Can get DIN mount ones which are 1 module in size which will fit nicely in a 6 way DB. Bigger DB for some wire space

        Sent from my CPH2565 using Tapatalk

        Comment

        • Derlyn
          Platinum Member

          • Mar 2019
          • 1748

          #5
          Originally posted by Dylboy
          Good idea for the contractors.

          As far as I know you can have 3 power supplies to the switch however they have to be the same phase.. you may be able to do different phases but warming stickers need to be there that there is 400volts. However need to check the book as even that may be a no go.

          The safest route I reckon is contactors. Can get DIN mount ones which are 1 module in size which will fit nicely in a 6 way DB. Bigger DB for some wire space

          Sent from my CPH2565 using Tapatalk
          Thanks. A contactor is not an option because they still need to switch the 3 rows of lights each on and off independantly.
          There are 3 circuit breakers on the same phase fed from ELR.

          Comment

          • Dylboy
            Gold Member

            • Jun 2020
            • 777

            #6
            Can do a contactor for each but as they the same phase then I am 99% sure ok to have the feeds into a light switch, will try find the regs if anything funny about it. Got a new phone and lost my PDF files so need to try get them back onto the phone for quick searching.

            Sent from my CPH2565 using Tapatalk

            Comment

            • GCE
              Platinum Member

              • Jun 2017
              • 1473

              #7
              I would go with Isetech suggestion - Piece of 4 core surfix with 3 switches and 3 x 1 module lighting contactors - You get the onesto 1 which is one module - A SP CB can control the control circuit

              If you go with the 3 lives they will need to be 3 pieces of cable as each has it's own CB or a triple pole CB so you can isolate the 4 core cable , which to me is messy

              If I look at regs 6.14.1.8 would be the one you want but 6.14.1.7 could be relevant

              SANS 10142 Ed3.1

              [B]6.14.1.7 [/B]If more than one phase in a lighting circuit is brought into one
              enclosure for switching purposes,
              a) labels (see 4.2) stating that the voltage between phase conductors could
              exceed 250 V shall be fixed in a visible position inside the enclosure (not
              on the cover plate); or
              b) the phase terminals in the enclosure shall be separated by suitable
              barriers.
              NOTE To avoid nuisance tripping where earth leakage protection is used, it is
              advisable to restrict the number of discharge luminaires on a circuit.


              6.14.1.8 If more than one circuit is brought into an enclosure, a warning label
              shall be fixed inside the enclosure.

              Comment

              • Derlyn
                Platinum Member

                • Mar 2019
                • 1748

                #8
                Thank you gentlemen for all your valuable contributions. Contactors it shall be with a 4 core going to the switch. Sorted.
                👍👍

                Comment

                • Derlyn
                  Platinum Member

                  • Mar 2019
                  • 1748

                  #9
                  Just thinking. Has anyone ever seen any labels in a bonding tray in the attic ? Multiple circuits into one enclosure. I haven't.

                  Comment

                  • Isetech
                    Platinum Member

                    • Mar 2022
                    • 2274

                    #10
                    No, and I doubt you ever will.


                    Originally posted by Derlyn
                    Just thinking. Has anyone ever seen any labels in a bonding tray in the attic ? Multiple circuits into one enclosure. I haven't.
                    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.