OR so I thought.
A site visit on Monday last week revealed what looked like someone had been to site to carry out a test report.
Simple things like labels seemed correct, a couple new weather proof socket outlets installed, new pool DB, no exposed wire and junction boxes, the usual stuff.
I did find a junction box outside which was not weather proof, but hey, the lid was secured and everything else looked, ok.
I received a copy of the COC, it looked legit, MIE, ECA member and all.
To my disappointment, I really thought this was going to be the one.
IF your name is Wesley, considering you work for a property inspection group, I really expected this to be the first.
YOu need to tick continuity of bonding and resistance of earthing at all points is compliant.
Last time I checked, if your insulation resistance recorded as 0.2 ohms, its a fail ( I am sure someone will correct me if this has changed since I last checked)
I must say a huge improvement from others I have seen.
Once again, random checks should be done on all COC's
I am sure it is a legal document.
A site visit on Monday last week revealed what looked like someone had been to site to carry out a test report.
Simple things like labels seemed correct, a couple new weather proof socket outlets installed, new pool DB, no exposed wire and junction boxes, the usual stuff.
I did find a junction box outside which was not weather proof, but hey, the lid was secured and everything else looked, ok.
I received a copy of the COC, it looked legit, MIE, ECA member and all.
To my disappointment, I really thought this was going to be the one.
IF your name is Wesley, considering you work for a property inspection group, I really expected this to be the first.
YOu need to tick continuity of bonding and resistance of earthing at all points is compliant.
Last time I checked, if your insulation resistance recorded as 0.2 ohms, its a fail ( I am sure someone will correct me if this has changed since I last checked)
I must say a huge improvement from others I have seen.
Once again, random checks should be done on all COC's
I am sure it is a legal document.