    Split conduit for the solar wires

    I am busy planning a new panel installation, We using 4 mm solarflex cables which has all the correct standards for UV, double insulated etc.

    There are a few option for getting the wire into the roof, either flatten a piece of conduit which is not flexible and fight with it or use sprague which is also not idea because when you try flatten it, it makes it more of a challenge to push the wires.

    Why not just use split conduit, its black, UV stable and easy to push the wires and fits in an adaptor with a bit of rubber tape and considering the solarflex wire doesn't even need to be in a conduit due to the fact that it is double insulated, it offer a little protection when the roof tile is put back in place.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
  • Douggie
    New Member
    • Sep 2021
    • 3

    #2
    Question: Using the black split conduit. Is it compliant in SA to use it everywhere? High Rise buildings etc.?

    Comment

    • GCE
      Platinum Member

      • Jun 2017
      • 1473

      #3
      Originally posted by Isetech
      I am busy planning a new panel installation, We using 4 mm solarflex cables which has all the correct standards for UV, double insulated etc.

      Why not just use split conduit, its black, UV stable and easy to push the wires and fits in an adaptor with a bit of rubber tape and considering the solarflex wire doesn't even need to be in a conduit due to the fact that it is double insulated, it offer a little protection when the roof tile is put back in place.
      I disagree with your statements - Solar wire is unamoured and single core and must therefore be in a wireway as per reg pasted below

      SANS10142-1 ed3.1
      6.4.6.1 Unarmoured single-core cables without a metal sheath shall only be
      used
      a) in wireways (see 6.5),

      3.85
      wireway

      open or enclosed route or support such as a rack, tray, ladder, ducting,
      trunking, sleeving or conduit that is intended to contain conductors or cables



      There are a few option for getting the wire into the roof, either flatten a piece of conduit which is not flexible and fight with it or use sprague which is also not idea because when you try flatten it, it makes it more of a challenge to push the wires.
      You cannot flatten it according to regs

      From Sans10142-1 ed3.1
      6.5 Wireways
      6.5.1 General
      6.5.1.1 When a wireway is installed
      i) no part of the wireway shall be flattened, split or damaged;

      Comment

      • GCE
        Platinum Member

        • Jun 2017
        • 1473

        #4
        Originally posted by Douggie
        Question: Using the black split conduit. Is it compliant in SA to use it everywhere? High Rise buildings etc.?
        There used to be reference made that no split conduit can't be used - I don't find a reference but would think split conduit does not comply to SANS 950


        SANS 950, Non-metallic conduit fittings for use in electrical installations.
        Last edited by GCE; 23-Apr-24, 02:52 PM. Reason: can should have been can't

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #5
          Solar wire is double insulation and is not required to be in a wireway, just imagine trying to fit solar panel wires in a wireway, not going to happened even if somebody does come come up a with a ridiculous code like the euro plug.

          Let me get my popcorn....every single solar installation will fail.
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #6
            Let me ask this question, do you have to install trailing cable in a wireway ?
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            • Isetech
              Platinum Member

              • Mar 2022
              • 2274

              #7
              I think we should first identify the type of wire used, the application it was designed for and how it must be installed.

              By the way the flattened 25 mm conduit works the best.

              I use a hot air gun, put the 25 mm pipe in the vice and squash it, check the wires can be fed easily through the piece of conduit. Put a 45 bend on the piece of pipe, attach a coupling and sprag. It offers additional mechanical protection for the double insulated solaflex wires, designed specifically for solar installations.

              If you have a better solution please share.


              6.4.6 Unarmoured cables

              6.4.6.1 Unarmoured single-core cables without a metal sheath shall only be used

              a) in wireways (see 6.5),

              b) for open wiring (see 6.4.5), and (if you go to 6.4.5 you will notice that it states that the voltage must not exceed the voltage)

              c) for temporary wiring (see 7.8).

              What this tells me is that these regs are not suitable for the solar installation application, once again we look forward to regs which are specifically applicable for the application.

              From my understanding of the regs, the new regs will only apply to new installations, all the older installation will apply to the old regs.

              IF your solar installtion was done in 2019, the new regs will not apply, not even if you sell the property.
              Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

              Comment

              • GCE
                Platinum Member

                • Jun 2017
                • 1473

                #8
                Originally posted by Isetech
                Solar wire is double insulation and is not required to be in a wireway, just imagine trying to fit solar panel wires in a wireway, not going to happened even if somebody does come come up a with a ridiculous code like the euro plug.

                Let me get my popcorn....every single solar installation will fail.
                SANS 60364-7-712 allows for the module wiring to be strapped with UV protected cable ties
                Double insulated single core cables can be run in the same wireway , single insulated needs to be run in separate conduits - Have a look at Table 712.9 in SANS 60364-7-712


                712.521.104 String wiring
                In the case where wiring of PV strings between modules is not protected by conduit or other
                enclosures, in addition to the requirements for all array wiring the following requirements shall
                also apply:
                • cables are protected from mechanical damage, and
                • the cable is so installed as to relieve tension in order to prevent the conductor from
                coming free from the connection.

                Comment

                • Isetech
                  Platinum Member

                  • Mar 2022
                  • 2274

                  #9
                  At least this clears up the original question, you can use split conduit to for added protection.

                  It also clears up the talk about the double insulated cables in the same wireway. To add to the confusion, what about the single insulated 6 mmsq earth wire installed in the same conduit, I see most installers have a single insulated earth wire inside the same wireway ?


                  Originally posted by GCE
                  SANS 60364-7-712 allows for the module wiring to be strapped with UV protected cable ties
                  Double insulated single core cables can be run in the same wireway , single insulated needs to be run in separate conduits - Have a look at Table 712.9 in SANS 60364-7-712


                  712.521.104 String wiring
                  In the case where wiring of PV strings between modules is not protected by conduit or other
                  enclosures, in addition to the requirements for all array wiring the following requirements shall
                  also apply:
                  • cables are protected from mechanical damage, and
                  • the cable is so installed as to relieve tension in order to prevent the conductor from
                  coming free from the connection.
                  Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                  Comment

                  • GCE
                    Platinum Member

                    • Jun 2017
                    • 1473

                    #10
                    Originally posted by Isetech
                    At least this clears up the original question, you can use split conduit to for added protection.
                    Apoligies - it does not clear it can should have been can't - was a typo

                    Comment

                    • GCE
                      Platinum Member

                      • Jun 2017
                      • 1473

                      #11
                      Originally posted by Isetech
                      At least this clears up the original question, you can use split conduit to for added protection.

                      It also clears up the talk about the double insulated cables in the same wireway. To add to the confusion, what about the single insulated 6 mmsq earth wire installed in the same conduit, I see most installers have a single insulated earth wire inside the same wireway ?
                      You need to understand the logic behind the regulations - The reason for running positive and negative in th esame wireway as earth is for in case of arching the neg or live can short to earth and the inverter will detect the fault and switch off

                      Wire ways are still under consideration under SANS60364-7-712 - SANS 10142-1 is clear on using a wireway

                      712.527 Selection and erection of wiring systems to minimize spread of fire
                      Under consideration.

                      Comment

                      • GCE
                        Platinum Member

                        • Jun 2017
                        • 1473

                        #12
                        The unfortunate part with the way people read regulations is to suit themselves - muddy the water and confuse everyone so that all an sundry then say there are no regulations for solar installs.

                        Solar install is the same as normal wiring besides there being one or two other points which are clarified under DC .

                        We been installing DC systems from early days with motors , UPS battery systems etc

                        Comment

                        • GCE
                          Platinum Member

                          • Jun 2017
                          • 1473

                          #13
                          Originally posted by Douggie
                          Question: Using the black split conduit. Is it compliant in SA to use it everywhere? High Rise buildings etc.?
                          Further to my previous post on split conduit and having a think on it

                          SANS10142-1 clause 6.5.1.1 i) would answer that one as well


                          6.5.1.1
                          i) no part of the wireway shall be flattened, split or damaged;

                          Comment

                          • Isetech
                            Platinum Member

                            • Mar 2022
                            • 2274

                            #14
                            From what I understand, you have to have protection where the solar wire and earth exits the roof, which means you need some form of protection, what wireway do you use?

                            Why dont we install twin+E in a wireway, because it is double insulated?

                            I am trying to wrap my head around the logic, its been a hectic 2 weeks of challenges with high end NVR's and IP cameras, software, firmware, another 5 hours in meetings today trying to resolve challenges and slow networks.





                            Originally posted by GCE
                            Further to my previous post on split conduit and having a think on it

                            SANS10142-1 clause 6.5.1.1 i) would answer that one as well


                            6.5.1.1
                            i) no part of the wireway shall be flattened, split or damaged;
                            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                            Comment

                            • GCE
                              Platinum Member

                              • Jun 2017
                              • 1473

                              #15
                              Originally posted by Isetech
                              From what I understand, you have to have protection where the solar wire and earth exits the roof, which means you need some form of protection, what wireway do you use?

                              .
                              There are manufactured units designed for different roof structure exits - We prefer taking the conduit over the edge of the roof with a drip loop into a junction box with a breather at the bottom before entering the roof space .
                              It stops any water ingress and damage to undertile waterproofing .