I noticed in the recently published (and retracted) SANS 10142-1-2 that the spec requires metal conduit to be used for DC cables. I have only ever seen standard PVC and trunking being used. This would mean that my installation would not comply. And looking at some of the photos of installs on the forums, 99% of them would fail too. Thoughts?
My understanding of the above is that IF conduit is used instead of running the cables bare, that conduit MUST be metal?
5.3 Integrated System Requirements > 5.3.5 Bonding > 5.3.5.2 Inverter-based Generation Earthing
c) Conduits
Where conduit is used for DC cables, it shall be metal conduit. Conduit shall be bonded at all
junctions to ensure electrical continuity of the conduit. The metal conduit shall be bonded to earth at
a suitable location.
c) Conduits
Where conduit is used for DC cables, it shall be metal conduit. Conduit shall be bonded at all
junctions to ensure electrical continuity of the conduit. The metal conduit shall be bonded to earth at
a suitable location.
My understanding of the above is that IF conduit is used instead of running the cables bare, that conduit MUST be metal?