Correct me if I am wrong here, BUT the Earth/Neutral bond is only required when in Islanding mode(Incoming Power fail), not as a permanent connection.
Hence the relay pulling in during islanding mode, making the Load Neutral referenced to Earth in order that the ELU can pick up an earth fault. When the power from the grid is available the Neutral is joined to Earth by the power supplier either at the Transformer or DB box depending on the type of Earthing System for the respective site.
Hence the relay pulling in during islanding mode, making the Load Neutral referenced to Earth in order that the ELU can pick up an earth fault. When the power from the grid is available the Neutral is joined to Earth by the power supplier either at the Transformer or DB box depending on the type of Earthing System for the respective site.