Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
Reg 6.15.2.1 states that socket outlets rated at less than 16A shall not be used in an electrical installation.
Does that include the 5A plugs that are made for conduit round boxes ?
I find it best to read the complete clause - Unless otherwise allowed clears that one up and therefore Clause 6.14.1.4 and Clause 6.14.1.5 states 6 amp which means it is allow for in SANS 10142
6.15.2.1 Socket-outlets shall be rated in accordance with the intended load. Unless otherwise allowed in this part of SANS 10142, socket-outlets rated at
less than 16 A shall not be used in an electrical installation.
I find it best to read the complete clause - Unless otherwise allowed clears that one up and therefore Clause 6.14.1.4 and Clause 6.14.1.5 states 6 amp which means it is allow for in SANS 10142
6.15.2.1 Socket-outlets shall be rated in accordance with the intended load. Unless otherwise allowed in this part of SANS 10142, socket-outlets rated at
less than 16 A shall not be used in an electrical installation.
Thanks
I just didn't want to go through the whole regulation book to see if there were any references to 5 Amp plugs.
I dont find any, only 6 Amp.
I note also that a 6 Amp plug can be used with a 20 Amp circuit breaker (6.14.1.5)
Can someone please describe what a partially dedicated socket outlet is. (6.14.1.5)
Final question. Those small 5 Amp plugs ...... What are they? 164-0, 164-1, 164-2, 164-3 Google doesn't want to help me.
What do you think about using a 5 amp unswitched plug for a small extractor in a bathroom?
At one stage it was not allowed , but changed in Ed 3 , I think.
It is now allowed as per 6.16.4.3 if switched with the lights.
6.16.4.3 Extraction fans
Where an extraction fan supply is switched with a luminaire, it shall be
connected to the switched portion of the light circuit, provided that the fan
circuit is connected by means of a SANS 164-3 or SANS 164-2-1 or
SANS 164-2-2 socket-outlet or a switch disconnector
Interesting, I have always called it a 5 amp plug. It seems even as far back as 2008, it was referred to as a 6 amp plug. I assume we are talking about he same thing?
Copied from an older version of the SANS regs.
"SANS 10142-1:2008
Edition 1.6
(As amended 2006 and 2008)
b) supplies one luminaire only, not exceeding the rating of the socketoutlet,
c) is accessible for maintenance purposes, and
d) is within 3 m of the luminaire that it supplies.
6.14.1.5 A lighting circuit that incorporates 6 A socket-outlets or 13 A socketoutlets
in accordance with 6.14.1.4 shall be protected by a circuit-breaker of
not exceeding 20 A. Lighting circuits that incorporate 13 A (fused plug top)
socket-outlets shall not be installed in a residential installation. Amdt 5"
Interesting, I have always called it a 5 amp plug. It seems even as far back as 2008, it was referred to as a 6 amp plug. I assume we are talking about he same thing?
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.