Earth leakage trips everytime loadshedding ends

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • rodga
    Junior Member
    • Nov 2021
    • 10

    #1

    [Question] Earth leakage trips everytime loadshedding ends

    Hi All

    With my limited electrical knowledge Ive been trying to figure out what could be causing this issue. Every time load shedding period ends and the power is restored, the earth leakage trips. This is fine when someone is at home and its the middle of the day, so it can just be switched on again. But its a real pain when we are not home or we have LS during the middle of the night, I usually wake up to switch everything on again so the fridge and bedroom fans can go back on.

    I have had 2 "electricians" out here in the last few months. The first said that the earth leakage circuit breaker is faulty and its needs to be replaced. So we did that and it changed nothing. Then he said the whole house needs to be rewired. All the while not providing any actual reasons/causes for this issue. The second guy at least had an earth leakage tester but did not pick up anything out of the ordinary. He recommended moving the geyser, stove and outside lights of the earth leakage. I was at first unsure, but after reading some discussions it seems that these devices are not required to go via a ELCB. But I said I will call him when Im ready.

    So to avoid spending any more money on something that may or may not work, or just moving things off the ELCB and therefore basically ignoring the issue, I want to get an electrician that has the correct equipment and knowledge to properly diagnose the issue before going ahead with a solution. Please help me find this person, Im based in Centurion so anyone in the area would be first prize.
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    Hi there Rodga

    To me it seems the house as a lot of "natural " earth leakage. So when power comes on and everything starts then the leakage is all at the same time.

    New regs cant take geysers of ELU (earth leakage device). But I recommend getting a second ELU and split the board so the adding of the natural earth leakage is limited and split between each ELU.

    If that does not work I would get the circuits insulated resistance tested to see if there is any breakdown.

    I am away the next 2 weeks but hopefully someone closer can take a look.

    Once back and not sorted will see of the boss is happy to take a trip with me to you to try see what we can do.

    Also maybe someone wiser than me may have a better idea of what could be happening




    Sent from my SM-N960F using Tapatalk

    Comment

    • rodga
      Junior Member
      • Nov 2021
      • 10

      #3
      Originally posted by Dylboy
      Hi there Rodga

      To me it seems the house as a lot of "natural " earth leakage. So when power comes on and everything starts then the leakage is all at the same time.

      New regs cant take geysers of ELU (earth leakage device). But I recommend getting a second ELU and split the board so the adding of the natural earth leakage is limited and split between each ELU.

      If that does not work I would get the circuits insulated resistance tested to see if there is any breakdown.

      I am away the next 2 weeks but hopefully someone closer can take a look.

      Once back and not sorted will see of the boss is happy to take a trip with me to you to try see what we can do.

      Also maybe someone wiser than me may have a better idea of what could be happening




      Sent from my SM-N960F using Tapatalk
      Thanks for the advice, I had that same thought of the leakage overwhelming the breaker when everything comes back on. Im sure I can reuse the old ELCB that was removed a few months ago too.
      Will definitely get in touch if I dont find someone before then.

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #4
        CBI earth leakage?

        I am hearing a lot of complaints about tripping earth leakage and alarms going off.

        I am convinced that both my hard drives are destroyed thanks to load shedding.

        You need a leakage current clamp ... I wish you luck trying to find a sparkie who carries one (@R4-6k for one) ... very few of us carry them.
        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • GCE
          Platinum Member

          • Jun 2017
          • 1473

          #5
          We have been finding that the surge arrestor type plug tops that are there to protect equipment are also causing problems when power comes back on after load shedding .
          The surge arrestor will take the spikes down to earth and the earth leakage sees it as a fault , which is correct , and it is doing it's job and so is the surge arrestor.

          Bit of a catch 22 situation

          A lot of the new fridges etc have mosfet's which are also doing it

          Best would be to install an extra ELU and put fridge etc on a dedicated circuit.

          Best way to test is unplug the fridge on the next load shed , maybe TV as well , computers , routers ,also any surge arrestor type plug tops and see if the problem disappears .

          Would be interested to hear the feed back.

          We have all the testers in the world , including a leakage current clamp , and have struggled on some of the intermittent faults of late.
          I had a query on Friday , with a 200Kva genset . On load shed to generator , everything fine , from genset back to mains the main CB trips instantly. Reset immediately and all is fine. I suggested disconnecting the surge arrestors as a test and have not heard back. Installation has not changed in the past 2 years , maybe the surge arrestors where getting tired or the inrush current settings on the CB had been adjusted or got tired.
          There are lot's of funny's happening at the moment and I have picked up that the frequency is jumping every 2 hours on sites that I can access and monitor. The sites are 300Km apart , so it is an Eskom thing.

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            I have a customer with those red plug tops on just about every extension plug ... no tripping issues.

            I rewired the building 3 weeks ago and fitted 2 earth leakage units per DB ... no CBI earth earth earth leakages were used on the site.

            the callouts I attended to recently ... all had CBI earth earth leakage units.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • Justloadit
              Diamond Member

              • Nov 2010
              • 3518

              #7
              Originally posted by GCE
              On load shed to generator , everything fine , from genset back to mains the main CB trips instantly. Reset immediately and all is fine.
              I am assuming that the genset is a diesel based one, and not the cheap 5kW V-0-V generators I suspect that there is a floating earth when connected to the genset, so when switching back to mains, the circuit is "charged" due to the floating period of time, and when connecting back to mains the "charge" is then discharged to earth tripping the ELU.
              Check that the generator Neutral is connected to earth with an earth resistor.
              Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
              Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

              Comment

              • Dylboy
                Gold Member

                • Jun 2020
                • 777

                #8
                Very good point on the surge arrestors. That is why now they want us to use a spark gap SPD for the Neutral. As the MOV can after time break down and leak to earth.
                Also they kinda say to install the MOV spd afyer ELU for that reason.

                Kicking my self for not thinking of that as done a fair bit of CPD stuff on it and slowly getting to grips... and having a whole lot more questions everytime I learn something hahaha.

                Sent from my SM-N960F using Tapatalk

                Comment

                • Derlyn
                  Platinum Member

                  • Mar 2019
                  • 1748

                  #9
                  I think most of us have been called out for similar problems earth leakage tripping at the resumption of power after loadshedding.

                  Here are my experiences.

                  1. Old Heineman 20mA earth leakage relays. Replaced earth leakage relay, problem solved.

                  2. Create your own load shedding with the main switch. If earth leakage trips then repeat process with a circuit isolated.

                  If fault persists then repeat with more circuits isolated until earth leakage does not trip when mains are turned on.

                  3. Install 2nd earth leakage and put all the circuits that were isolated, throufh it.

                  4. Do final testing.

                  The above method has solved the problem everytime for me.

                  We must remember that there are sometimes huge surges when power is switched on after loadshedding which aggrevate the situation.

                  The neatest solution I have personally seen to avoid any power surges after loadshedding is to take the mains through a contactor that is energised by a delay on timer so that your power only comes on a minute or two after everyone else's. By the time your power comes on then all those nasty surges have already done their thing to everyone else.

                  Sorry for the long essay

                  Peace out .. Derek

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #10
                    If you are going to go to that expense ... I would strongly advise you instal a trip connect unit ... it will prevent the contactor reenergising and a time can be set on the unit ... if the neutral is missing resulting in higher than normal voltage (600+ VAC)

                    From years of experience with load shedding ... it will stop in a couple weeks ... everyone forgets about it ... then suddenly it is at the top of everyone's list again ... generator sales go through the roof ... battery inverter prices go crazy and so the cycle just goes round and round.

                    A little forward panning will not only save a ton of cash ... but also prevent issue with your electronics ... which might not fail today or tomorrow ... but will fail sooner or later.
                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • rodga
                      Junior Member
                      • Nov 2021
                      • 10

                      #11
                      Apologies took a bit of a break thanks to load shedding

                      Originally posted by ians
                      I have a customer with those red plug tops on just about every extension plug ... no tripping issues.

                      I rewired the building 3 weeks ago and fitted 2 earth leakage units per DB ... no CBI earth earth earth leakages were used on the site.

                      the callouts I attended to recently ... all had CBI earth earth leakage units.
                      The old ELU was not a CBI and had the same issue. Still have it in the garage so will take a pic later.


                      Originally posted by Dylboy
                      Very good point on the surge arrestors. That is why now they want us to use a spark gap SPD for the Neutral. As the MOV can after time break down and leak to earth.
                      Also they kinda say to install the MOV spd afyer ELU for that reason.

                      Kicking my self for not thinking of that as done a fair bit of CPD stuff on it and slowly getting to grips... and having a whole lot more questions everytime I learn something hahaha.

                      Sent from my SM-N960F using Tapatalk
                      What is an MOV and SPD?


                      Originally posted by Derlyn
                      I think most of us have been called out for similar problems earth leakage tripping at the resumption of power after loadshedding.

                      Here are my experiences.

                      1. Old Heineman 20mA earth leakage relays. Replaced earth leakage relay, problem solved. ELU was replaced with a new CBI, no change. Will use the old one to seperate the circuits on the earth leakage.

                      2. Create your own load shedding with the main switch. If earth leakage trips then repeat process with a circuit isolated.
                      If fault persists then repeat with more circuits isolated until earth leakage does not trip when mains are turned on.

                      Have tried this before, but it does not reproduce the problem. Will try it again though.


                      3. Install 2nd earth leakage and put all the circuits that were isolated, throufh it. Will reuse the old one

                      4. Do final testing.

                      The above method has solved the problem everytime for me.

                      We must remember that there are sometimes huge surges when power is switched on after loadshedding which aggrevate the situation. I do think this may be the issue

                      The neatest solution I have personally seen to avoid any power surges after loadshedding is to take the mains through a contactor that is energised by a delay on timer so that your power only comes on a minute or two after everyone else's. By the time your power comes on then all those nasty surges have already done their thing to everyone else. Do you perhaps have a link to such a device?

                      Sorry for the long essay

                      Peace out .. Derek
                      Originally posted by ians
                      If you are going to go to that expense ... I would strongly advise you instal a trip connect unit ... it will prevent the contactor reenergising and a time can be set on the unit ... if the neutral is missing resulting in higher than normal voltage (600+ VAC) Link please. I would like to research as much as possible so I at least know what the electrician is talking about when they do come. lol

                      From years of experience with load shedding ... it will stop in a couple weeks ... everyone forgets about it ... then suddenly it is at the top of everyone's list again ... generator sales go through the roof ... battery inverter prices go crazy and so the cycle just goes round and round.

                      A little forward panning will not only save a ton of cash ... but also prevent issue with your electronics ... which might not fail today or tomorrow ... but will fail sooner or later.
                      Just to add, this issue has been present since we moved in 2017 so it is not something that started after I added something to system.

                      Thanks for all the comments thus far.

                      Comment

                      • rodga
                        Junior Member
                        • Nov 2021
                        • 10

                        #12
                        Missed this one in my multi quote

                        Originally posted by GCE
                        We have been finding that the surge arrestor type plug tops that are there to protect equipment are also causing problems when power comes back on after load shedding .
                        The surge arrestor will take the spikes down to earth and the earth leakage sees it as a fault , which is correct , and it is doing it's job and so is the surge arrestor.

                        Bit of a catch 22 situation

                        A lot of the new fridges etc have mosfet's which are also doing it

                        Best would be to install an extra ELU and put fridge etc on a dedicated circuit.

                        Best way to test is unplug the fridge on the next load shed , maybe TV as well , computers , routers ,also any surge arrestor type plug tops and see if the problem disappears .

                        Would be interested to hear the feed back. I think I only have one of these surge arrestors but will check it out, and will let you know what happens

                        We have all the testers in the world , including a leakage current clamp , and have struggled on some of the intermittent faults of late.
                        I had a query on Friday , with a 200Kva genset . On load shed to generator , everything fine , from genset back to mains the main CB trips instantly. Reset immediately and all is fine. I suggested disconnecting the surge arrestors as a test and have not heard back. Installation has not changed in the past 2 years , maybe the surge arrestors where getting tired or the inrush current settings on the CB had been adjusted or got tired.
                        There are lot's of funny's happening at the moment and I have picked up that the frequency is jumping every 2 hours on sites that I can access and monitor. The sites are 300Km apart , so it is an Eskom thing.

                        As per my previous post, this issue has been here since we moved here in 2017

                        Comment

                        • AndyD
                          Diamond Member

                          • Jan 2010
                          • 4946

                          #13
                          Originally posted by GCE
                          We have been finding that the surge arrestor type plug tops that are there to protect equipment are also causing problems when power comes back on after load shedding .
                          The surge arrestor will take the spikes down to earth and the earth leakage sees it as a fault , which is correct , and it is doing it's job and so is the surge arrestor.

                          Bit of a catch 22 situation

                          A lot of the new fridges etc have mosfet's which are also doing it

                          Best would be to install an extra ELU and put fridge etc on a dedicated circuit.

                          Best way to test is unplug the fridge on the next load shed , maybe TV as well , computers , routers ,also any surge arrestor type plug tops and see if the problem disappears .

                          Would be interested to hear the feed back.

                          We have all the testers in the world , including a leakage current clamp , and have struggled on some of the intermittent faults of late.
                          I had a query on Friday , with a 200Kva genset . On load shed to generator , everything fine , from genset back to mains the main CB trips instantly. Reset immediately and all is fine. I suggested disconnecting the surge arrestors as a test and have not heard back. Installation has not changed in the past 2 years , maybe the surge arrestors where getting tired or the inrush current settings on the CB had been adjusted or got tired.
                          There are lot's of funny's happening at the moment and I have picked up that the frequency is jumping every 2 hours on sites that I can access and monitor. The sites are 300Km apart , so it is an Eskom thing.
                          Surge arrestors would be worth ruling out, it's possible there could be a voltage spike on power reset that's causing them to conduct. I think some earth leakages are more prone to tripping due to phase shift that could be occuring momentarily when power comes back on and the load isn't linear. Same with harmonics...

                          I've had several cases where earth leakages trip and they're testing fine on a full ramp and function test but replacing them with a different make has sorted out the problem. Not loadshedding related but I've also a problem where an earth leakage was tripping once a day and every day around suppertime. I eventually proved it happened every time the streetlight right outside the property switched on even though the streetlights were on a different supply and nothing to do with the house supply. It turned out that particular RCD was sensitive to harmonics from the inductive ballast and starter.
                          _______________________________________________

                          _______________________________________________

                          Comment

                          • ians
                            Diamond Member

                            • Apr 2010
                            • 3943

                            #14
                            I think we have discussed those little red mother F^&*ers in the past (ellie surge plug tops) ... they have cause many wasted hours trying to trace intermittent faults (not related to load shedding) ... just random tripping ... using the 250 Volt setting on the insulation resistance test ... identifies that issue quickly.
                            Comments are based on opinion...not always facts....that's why people use an alias.

                            Comment

                            • Derlyn
                              Platinum Member

                              • Mar 2019
                              • 1748

                              #15
                              @Rodga

                              The fact that you cannot re create the fault with the main switch seems to indicate that the fault is NOT on your installation but is caused by an unwanted characteristic on the supply when switched on by the supplier after loadshedding.

                              What that characteristic is, is hard to say, but I suppose it is either spikes, high voltage or something luke that in which case the delayed energising of your supply by means of a contactor will solve the problem.

                              I do not know of a plug and play unit available but one can make up a unit using a contactor and a fridge safe unit that is sold by Ellies. Install a dedicated plug close to the db that is supplied directly from the main switch through the necessary circuit breaker.

                              Now plug the fridge safe unit into that plug. When the power comes on after loadshedding, this unit checks the supply for any abnormalities before turning on the output. This output is used to energise the contactor that turns the mains on to everything else including the earth leakage relay. The fridge safe has a monitoring period of about 3 minutes so your load shedding will be 3 minutes longer than your neighbours.

                              There is the added advantage that this unit constantly checks the supply and should there be any abnormality at any time, it will disconnect your installation from the supply and re connect automatically again after 3 minutes should the supply be back to normal.

                              Hope this helps

                              Peace out .. Derek.