    LED 4 ft and 5 ft tube wiring

    I have been doing a number of "conversions" to standard 5 ft fittings... cut out all the control gear and wire directly to the lamp holder.

    While testing a brand new faulty tube (pioLED) at my local wholesaler the salesman told me the power was at the top of the fitting ..."BANG" it seemed as though load shedding had kicked in with a bang.

    Which brings me to modifying and wiring of fittings... it seems that PioLED have a resistor on one side of the tube which results in a bang if the tube is installed the wrong way.

    I watched a few videos on how people convert fittings and seems some people run and earth wire to the non power side of the fitting.

    What are your thoughts?
    Comments are based on opinion...not always facts....that's why people use an alias.
  • ians
    Diamond Member

    • Apr 2010
    • 3943

    #2
    No spec or data sheets...no wiring no certification or approval ...am i missing something ?


    Being the Pioneers of LED Lighting, it is our duty to set the industry standard for all LED advancements. We look forward to making an ever-lasting impression on you with our exceptional Quality and Service.
    Comments are based on opinion...not always facts....that's why people use an alias.

    Comment

    • ians
      Diamond Member

      • Apr 2010
      • 3943

      #3
      Can anyone explain to me why they fit a bridge across the one end of the tube which causes the circuit breaker to trip.

      Should the exposed type of lamp holder be used for this type of lamp...the one i am referring to is the one were the brass connections are exposed...the plastic cover holders should only be used ?

      Another very concerning factor to take into account...a bridge which looks like a starter.

      While visiting a wholesaler the other day i noticed a DIY customer purchasing an LED 5 ft lamp...which comes with a "starter" ...the salesman informed the customer that he could just remove the old lamp and starter and replace it with the LED lamps and starter.

      This got my interest because i havent seen that before ...i would normal remove all the internal components wire the lampholders directly to the 230 terminals and bingo light works ...if you insert the tube the right way...one of the reason i always label the power side...i was going to wire both sides...to make it easy for the customer ...however this proved to be a problem if pioLED lamps are used.

      Someone mentioned that the "starter" bridge is actually a fuse...which brings me to the next question...shouldnt it be compulsory to fit a fuse in line with the tube?
      Comments are based on opinion...not always facts....that's why people use an alias.

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #4
        An LED driver ....wohoooo this special component required for LED lights...so what is an LED driver?

        A simple transformer...capacitor and bridge rectifier?

        I think it is time to take out my dremmel and cut a few drivers and tubes to see what all the fuss is about.

        I had an enquiry for a few hundred LED fittings...so i shopped around and found a really expansive LED fitting...you know...thinking more expansive...better quality and all the jazz... i was told the driver was the brains of the fitting and they used a driver imported from Germany...i compared it to nordland (who i have always trusted to be the lasted and best quality...especially when talking weather proof ...however there LED chips couldnt compare) so we spent R485 000 on a shipment of LED fittings for a factory ...installed them and imagine that 2 failed on start up...so i removed the fitting (very simple installation method...just pop off the clip on the top) ad decided to open it...the driver was the same as all the other drivers i had used on all the other LED fittings i have installed in the past.

        Customers always ask ...what happens when the fitting stops working...my response would be... well you have to replace the entire fitting... however this is not entirely true anymore...you can get spares and replace the driver and LED module.
        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #5
          I learnt something new today...

          Got a response from pioLED...much appreciated.

          They have international certifications of EMC and LVD for their T8 LED tubes...I have no idea what that means or if it is valid for use in SA...It seems we no longer require SABS standards for products we install in SA...these guys sell thousands if not hundreds of thousands of light fittings in SA.

          I assume we just get these certificates from them and attach it to our COC once the project is complete and tested.

          With regards to modifying a standard old 4/5 ft fluorescent to an LED... i have always ....just stripped the entire fitting and rewired it with 230 volts on one side and no wiring on the opposite side.

          The drawings i received from pioLED clearly show 2 different methods of rewiring the fittings...which explains why the other side of the tube is bridged.

          1 - You just strip everything and connect to one side of the fitting.

          2 - You dont strip the wires...you just bridge out the ballast ...remove the starter and fit the LED "starter" (which in some cases is a fuse and others it is a just a bridge...depending on the lamp supplier)
          The neutral goes onto one pin...the live goes to the opposite side lampholder through the lamp (which is why it is bridged on the opposite side) through the bridge/fuse "starter" and back onto the other side of the lamp.

          I actually prefer the second option if a fuse is used in place of the starter....and it saves time stripping the light then rewiring it...will be doing this in future.

          Google search converting a fluorescent light to led...there are plenty diagrams.
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            I am really liking these end caps... there is no longer a need for a light fitting to hold switch gear or create a reflective surface as the led only have a certain degree/angle of light...these look neat and practical.

            ooops cant seem to paste the pic.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • GCE
              Platinum Member

              • Jun 2017
              • 1473

              #7
              Hi

              Retro fitting fluorescent fittings with LED tubes means rewiring the fitting.The minute you rewire the fitting you become the manufacturer and all the insurances and risks become yours.

              You need to comply to ARP 032 - 2014

              To migrate the risk it is cheaper to buy a channel that has been specifically wired for LED tubes - There is a minefield in the document.

              The installation regulations SANS 10142 prescribe that only SABS approved equipment may be installed in an electrical installation. The moment it is altered, changed or modified from the original design there is no way of ensuring compliance unless you follow the Approved Recommended Practice (ARP 032 – 2014 which consists of 6 sections), or an applicable approved standard. That means as soon as you retrofit the fitting you are as liable as the manufacture of the original product. You need to ensure that you carry out the tests as prescribed in the Code on this work done by you.

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #8
                Originally posted by GCE
                Hi

                Retro fitting fluorescent fittings with LED tubes means rewiring the fitting.The minute you rewire the fitting you become the manufacturer and all the insurances and risks become yours.

                You need to comply to ARP 032 - 2014

                To migrate the risk it is cheaper to buy a channel that has been specifically wired for LED tubes - There is a minefield in the document.

                The installation regulations SANS 10142 prescribe that only SABS approved equipment may be installed in an electrical installation. The moment it is altered, changed or modified from the original design there is no way of ensuring compliance unless you follow the Approved Recommended Practice (ARP 032 – 2014 which consists of 6 sections), or an applicable approved standard. That means as soon as you retrofit the fitting you are as liable as the manufacture of the original product. You need to ensure that you carry out the tests as prescribed in the Code on this work done by you.
                Interesting.

                Do you know of a company which has an SABS approval ?
                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • bergie
                  Email problem

                  • Sep 2010
                  • 308

                  #9
                  i ordered some vapourloom weather proof fittings from ARB. the type prewired for LED lamps. they come without the internal plastic cover so all wires just hang on the clear cover. and they cost more than the one with the electronic ballast.

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #10
                    Originally posted by bergie
                    i ordered some vapourloom weather proof fittings from ARB. the type prewired for LED lamps. they come without the internal plastic cover so all wires just hang on the clear cover. and they cost more than the one with the electronic ballast.
                    and did they have an SABS stamp of approval ?
                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • Derlyn
                      Platinum Member

                      • Mar 2019
                      • 1748

                      #11
                      Remember that electrical or electronic appliances do not have to physically bear the SABS stamp on them or the packaging to be SABS approved.

                      As long as they are covered by an SABS LOA ( letter of authority ) which the supplier must be able to produce, then it's A OK.

                      This last week I was requested to connect an electrical showerhead. There was no SABS stamp on the product or packaging so I insisted to see the LOA before doing the job. A valid LOA was produced so I proceeded.

                      Derek

                      Comment

                      • ians
                        Diamond Member

                        • Apr 2010
                        • 3943

                        #12
                        Originally posted by Derlyn
                        Remember that electrical or electronic appliances do not have to physically bear the SABS stamp on them or the packaging to be SABS approved.

                        As long as they are covered by an SABS LOA ( letter of authority ) which the supplier must be able to produce, then it's A OK.

                        This last week I was requested to connect an electrical showerhead. There was no SABS stamp on the product or packaging so I insisted to see the LOA before doing the job. A valid LOA was produced so I proceeded.

                        Derek
                        So we buy a LED fitting with an LOA ... copy the wiring size and lampholders and use the LOA for all your rewired fittings ?
                        Comments are based on opinion...not always facts....that's why people use an alias.

                        Comment

                        • Derlyn
                          Platinum Member

                          • Mar 2019
                          • 1748

                          #13
                          Originally posted by ians
                          So we buy a LED fitting with an LOA ... copy the wiring size and lampholders and use the LOA for all your rewired fittings ?
                          Hi Ians

                          You could if you are that way inclined.

                          That said, I don't think it will be worth the time and effort.

                          Besides, the LOA contains quite a comprehensive description of the appliance. ie. brand, make, model, etc. much like the Magneto emergency light sold by Builders that you were pushing a while back. No SABS stamp on product or packaging, but covered by a loa.

                          BTW, bought one a couple of days ago and tested. Brilliant product. Thanks for the heads up.


                          Derek
                          Last edited by Derlyn; 31-Oct-19, 06:40 AM.

                          Comment

                          • ians
                            Diamond Member

                            • Apr 2010
                            • 3943

                            #14
                            Originally posted by Derlyn
                            Hi Ians

                            You could if you are that way inclined.

                            That said, I don't think it will be worth the time and effort.

                            Besides, the LOA contains quite a comprehensive description of the appliance. ie. brand, make, model, etc. much like the Magneto emergency light sold by Builders that you were pushing a while back. No SABS stamp on product or packaging, but covered by a loa.

                            BTW, bought one a couple of days ago and tested. Brilliant product. Thanks for the heads up.


                            Derek
                            "that way inclined"

                            Lets clear up a few things... i started my business almost 29 years ago ... i did everything by the book ...and i mean everything...even joined the ECA (was a member for 10 years) ECB... DOL... WC etc etc ...the only bad thing I ever did was drive a little faster than i was suppose to ...always in rush... trying to keep customers happy... became an installation electrician ...then a master electrician... even got a code 14 license just in case i needed to drive a truck... started this business with a tool box i got on the railways when i did my apprenticeship and a 6 ft ladder i bought at wardkiss with money i got from selling my motor bike...I also used the money from the motor bike to buy a golf and a set of roof racks.

                            Because i had no business plan the bank manager laughed at me and told me i wouldnt last 5 years... which resulted in my application for vehicle finance being declined... back then a 1400 nissan was R18 000.00... including the canopy.

                            Did as many courses on what ever i could...from basic gate installations to PLC training... you name it... attended every amendment seminar offered ... inspection refresher courses.

                            Only used the best SABS products money could buy...heinemen breakers ...crabtree plugs then moved over to clipsal because crabtree had a sparking issue on their switches... moved over to clipsal... which is now just a piece plastic junk like MES ...horizon and all the rest... Lascon were the prefered lighting brand... klockner moeller and omron were the preferred automation products... etc etc etc.

                            now that we have that out the way...

                            All i have seen over the years is a general decline in workmanship and attitude towards the industry... new regs and new SABS books being published ...but until someone employs suitably skilled staff who actually go out into the field and perform their duties... it just gets worse by the day.

                            A comprehensive guide ... a steel box... 4 lampholders and a couple of pieces of wire...you dont even get a terminal block on new fittings.

                            Please post one so we can see it.
                            Last edited by ians; 31-Oct-19, 02:28 PM.
                            Comments are based on opinion...not always facts....that's why people use an alias.

                            Comment

                            • ians
                              Diamond Member

                              • Apr 2010
                              • 3943

                              #15
                              Originally posted by Derlyn
                              Hi Ians

                              the Magneto emergency light sold by Builders that you were pushing a while back. No SABS stamp on product or packaging, but covered by a loa.

                              BTW, bought one a couple of days ago and tested. Brilliant product. Thanks for the heads up.


                              Derek
                              By the way i dont sell them... I have a box full of them for my house ...site work you name it... best buy in a long time... it is something we have battled with for many years... if you got 2 hours out of a portable light in the past it was a winner... these light last days on site... i just need to find a decent headlamp which is rechargeable ...bright enough and has the battery backup or a means for quick swop.