Socket oulet in a laundry room

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Ishmaelmo
    Full Member
    • Apr 2018
    • 43

    #1

    [Question] Socket oulet in a laundry room

    Hi all,

    Is it allowed to install a socket outlet in a laundry room?

    I have a socket outlet mounted in my laundry room at a hieght of 150cm from the ground.
    They said, it can not be mounted on the same height as others because of water splashing, dripping, and and and.

    I want to know if it is allowed.
    Otherwise they must remove it.

    Thanks in advance.
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #2
    Hi

    There is no regulation preventing the mounting of sockets in a laundry room - You need to plug in the wash machine to do the laundry

    Be reasonable about the usage and positioning of the socket

    Comment

    • SeanM
      Bronze Member

      • Mar 2018
      • 120

      #3
      Morning Ishmaelmo

      In terms of the regulations it states that any socket within 2m of a water pipe must be on an earth leakage so in other words a normal socket is ok and a dedicated socket in not.

      Comment

      • Canuck
        New Member
        • Nov 2018
        • 8

        #4
        Although I am from Canada and have no experience in SA, I thought that I would jump in. I am not sure if your new regulations are in place yet but I think it says in 10142-1 (2017) any socket requires earth leakage protection (6.15 note) except ones for critical supply (6.7.5.5) If your general application of codes are similar to ours then I assume that if the sockets were installed under a previous code then the rules at that time would apply to its installation.

        Comment

        • Ishmaelmo
          Full Member
          • Apr 2018
          • 43

          #5
          Originally posted by GCE
          Hi

          There is no regulation preventing the mounting of sockets in a laundry room - You need to plug in the wash machine to do the laundry

          Be reasonable about the usage and positioning of the socket
          Alright!
          The positioning of our washing machine will be away from the socket outlet, say 1m away.
          And only washing machine will be connected on that socket outlet.

          Comment

          • Ishmaelmo
            Full Member
            • Apr 2018
            • 43

            #6
            Originally posted by SeanM
            Morning Ishmaelmo

            In terms of the regulations it states that any socket within 2m of a water pipe must be on an earth leakage so in other words a normal socket is ok and a dedicated socket in not.
            Uhm! I suppose is on earth leakage. Is bridged to other socket outlets.

            Comment

            • Ishmaelmo
              Full Member
              • Apr 2018
              • 43

              #7
              Originally posted by Canuck
              Although I am from Canada and have no experience in SA, I thought that I would jump in. I am not sure if your new regulations are in place yet but I think it says in 10142-1 (2017) any socket requires earth leakage protection (6.15 note) except ones for critical supply (6.7.5.5) If your general application of codes are similar to ours then I assume that if the sockets were installed under a previous code then the rules at that time would apply to its installation.
              Yes! They are in place. There was a thread discussing new regulations.
              We are learning everyday.

              Comment

              • Dave A
                Site Caretaker

                • May 2006
                • 22810

                #8
                Originally posted by Ishmaelmo
                I have a socket outlet mounted in my laundry room at a hieght of 150cm from the ground.
                They said, it can not be mounted on the same height as others because of water splashing, dripping, and and and.
                Out of curiosity, at what height are the other socket outlets mounted at?
                Participation is voluntary.

                Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                Comment

                • Ishmaelmo
                  Full Member
                  • Apr 2018
                  • 43

                  #9
                  Originally posted by Dave A
                  Out of curiosity, at what height are the other socket outlets mounted at?
                  They are at 50cm.
                  The kitchen socket outlets are between 130cm & 140cm.
                  Light swicthes I think is 150cm.

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #10
                    if you are concerned about the socket outlet...there are various option:

                    A weather proof socket in an enclosure or

                    an industrial type socket outlet with a lock ring (the blue 3 pins ones)

                    just a note...a washing machine is certainly not regarded as a critical application...and only a fool would consider not connecting earth leakage protection...however from my 38 years of experience in the electrical industry...anything is possible in Africa.
                    Comments are based on opinion...not always facts....that's why people use an alias.