  • Leecatt
    Silver Member

    • Jul 2008
    • 404

    #31
    I find that very interesting Dave. Thanks I'll look into it on the next few days
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

    Comment

    • ians
      Diamond Member

      • Apr 2010
      • 3943

      #32
      Just to add fuel, no juntion boxes are permitted in zone 0 - 1 - 2. So if you install a light on the wall you have to run surfix or twin + E directly to the light without a junction box, because in theory a round box behind the fitting would be classified as a junction box.

      Thanks to everyone contributing to this thread, i think i have just saved myself future complications. It made me read the black book (SANS) and i found some other things which needed attention with regards to the job i am busy with a present in the bathroom. Discussed it with the customer who agrees with me and will make suitable adjustments to overcome the problems.
      Last edited by ians; 24-Nov-14, 09:04 AM.
      Comments are based on opinion...not always facts....that's why people use an alias.

      Comment

      • ACEsterhuizen
        Bronze Member

        • Mar 2012
        • 165

        #33
        Dave, i have to break a nervous smile here...because it is all there in Section 9..... it says it has to comply "with the general safety principles of such standard" only.

        Comment

        • Dave A
          Site Caretaker

          • May 2006
          • 22810

          #34
          Originally posted by ACEsterhuizen
          it says it has to comply "with the general safety principles of such standard" only.
          Just point me to a definition of "the general safety principles" in either the installation regulations or in SANS 10124-1 and I'll be a happy man

          Second prize would be a definition from someone of authority - such as the Chief Inspector (DoL).
          Participation is voluntary.

          Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

          Comment

          • ACEsterhuizen
            Bronze Member

            • Mar 2012
            • 165

            #35
            Originally posted by Dave A
            Just point me to a definition of "the general safety principles" in either the installation regulations or in SANS 10124-1 and I'll be a happy man

            Second prize would be a definition from someone of authority - such as the Chief Inspector (DoL).
            Page 69

            " 5 Fundamental requirements
            NOTE This clause contains the general safety principles applicable to electrical
            installations. Amdt 5
            5.1 Safety
            5.1.1 Live parts
            It shall not be possible to......"

            Comment

            • Dave A
              Site Caretaker

              • May 2006
              • 22810

              #36
              So we agree we have to apply section 5 of SANS 10124-1 only (and such parts of the code referenced from within section 5 - e.g. main switch) when it comes to issuing a COC on an existing electrical installation.

              So now back to our open light fitting in the bathroom. According to sec. 7.1 we can't have it in there, but that falls outside of section 5
              Participation is voluntary.

              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

              Comment

              • ACEsterhuizen
                Bronze Member

                • Mar 2012
                • 165

                #37
                And also, what exactly is an "existing installation"?

                Comment

                • david2677
                  Junior Member
                  • Mar 2013
                  • 21

                  #38
                  The person who does the work should certify his/her workmanship, the fault reports is a recommendation for corrective measures that need to be instituted. That's my understanding of how its meant to be
                  Repeating a mistake is not a mistake, its a habit

                  Comment

                  • Dave A
                    Site Caretaker

                    • May 2006
                    • 22810

                    #39
                    Originally posted by ACEsterhuizen
                    And also, what exactly is an "existing installation"?
                    One that you haven't just installed yourself.
                    Participation is voluntary.

                    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                    Comment

                    • ians
                      Diamond Member

                      • Apr 2010
                      • 3943

                      #40
                      Anyone know where i can find a ip 55 light for a bathroom as per requirements for zone 1? That doesnt look like crap.
                      Comments are based on opinion...not always facts....that's why people use an alias.

                      Comment

                      • Justloadit
                        Diamond Member

                        • Nov 2010
                        • 3518

                        #41
                        I purchased this one recently from Radiant which includes a fan
                        Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                        Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #42
                          Sorry i should have specified, wall mounted unit.
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • Justloadit
                            Diamond Member

                            • Nov 2010
                            • 3518

                            #43
                            Best is to talk to a Radiant or a Eurolux distributor.
                            Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                            Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                            Comment

                            • DieterT
                              Bronze Member

                              • Oct 2014
                              • 126

                              #44
                              Can't believe I missed this topic.

                              Lots of interesting point of views and also interesting point Dave brings up.
                              From my point of view, the regs needs to be taken as a hole and not just one section and on the CoC at Section 4.13(b) it says i.e. section 5 of SANS 10142-1 thus saying to me that the rest of the regs needs also to comply.
                              Separate to that point which I will try and get an answer from the AIA, back to the question about the inspection report.

                              When a client contacts me in regards to a CoC I tell them that I first do an inspection based on issuing a CoC. Should everything comply I issue a CoC.
                              Should some small things be found it is communicated with the client and repaired on site (if not to large of an expense)
                              CoC is only issued once monies are paid in full (yes I do know you are not allowed to retain the CoC if no monies paid, but hey one have to have some form of bartering thus if client does not want to pay I was never there and he has to go through the same process with the next guy)

                              Ok so say lots of problems found I then invoice for the inspection and when monies paid in full I send the client a detailed quotation where I also clearly stipulate that should another contractor preform repairs a detailed inspection will have to be done again and the contractor needs to issue a CoC for any changes he has made.
                              So my workers preform the repairs once the quotation is excepted and deposit paid with my general control and I also then do the final visual inspection on their repairs and the necessary test (which probably would change with major repairs)

                              FYI, one cannot do the inspection give a report have another contractor come and do the work, come back and give a CoC. This defies the requirements of general control from the registered person. On the other hand, the contractor who implements to repairs needs to be properly registered in order to do electrical installation work as defined in the EIR so then why would this person not issue the CoC.
                              To strange...