    Distribution board over toilet

    No bath and no shower, but can you have the distribution board over the toilet?

    Click image for larger version

Name:	ielect pics 066.jpg
Views:	1
Size:	41.5 KB
ID:	268862

    The db is also about 2.2m away from the hand basin.

    Click image for larger version

Name:	ielect pics 067.jpg
Views:	1
Size:	43.0 KB
ID:	268863
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services
  • cejay
    Full Member

    • Feb 2011
    • 58

    #2
    I hope that,s not in a bar, nor at a club where Alch gets more than distribution and control... U never know someone might slip off his balance
    "IF YOU WAIT FOR PERFECT CONDITION, YOU'LL NEVER GET ANYTHING DONE"

    Comment

    • Justloadit
      Diamond Member

      • Nov 2010
      • 3518

      #3
      I suppose it is a smelly situation.
      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

      Comment

      • AndyD
        Diamond Member

        • Jan 2010
        • 4946

        #4
        As far as I know it wouldn't breach the regs apart from maybe being easily accessible for emergency supply isolation if the cubicle/bathroom is in use and locked.
        _______________________________________________

        _______________________________________________

        Comment

        • Dave A
          Site Caretaker

          • May 2006
          • 22807

          #5
          After some careful thought, we're going to apply

          6.6.1.7 A distribution board shall not be mounted

          c) within a radius of 1m from a water tap or valve (in the same room), unless the enclosure provides a degree of protection of at least IP44.

          The next question, given the design - would it be acceptable to insert a rubber strip to seal the door edge against the cover?
          Participation is voluntary.

          Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

          Comment

          • AndyD
            Diamond Member

            • Jan 2010
            • 4946

            #6
            Hmm, I thought the sink was 2 meters away so you must be referring to the toilet flush...which is plastic. To be honest I suspect the enclosure might be IP 44 as it stands even without a rubber door gasket. All the panels with door gaskets that I have in my stock are IP55 or better, I just checked. From what I can see in the photos I would just take a laissez faire stance on this one and give it the benefit of the doubt.

            Click image for larger version

Name:	untitled2.jpg
Views:	1
Size:	56.0 KB
ID:	261585
            _______________________________________________

            _______________________________________________

            Comment

            • Dave A
              Site Caretaker

              • May 2006
              • 22807

              #7
              Yep - it's the toilet cistern refill valve I'm concerned about. And I believe requiring IP44 is fair enough to cover water flying around if something went faulty there.

              Originally posted by AndyD
              To be honest I suspect the enclosure might be IP 44 as it stands even without a rubber door gasket.
              Thanks for that guidance - very helpful.
              Participation is voluntary.

              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

              Comment

              • AndyD
                Diamond Member

                • Jan 2010
                • 4946

                #8
                You're welcome Dave. Did the setup in the photos pass muster 'as is' or is it still a contentious issue?
                _______________________________________________

                _______________________________________________

                Comment

                • Dave A
                  Site Caretaker

                  • May 2006
                  • 22807

                  #9
                  Nope, the photos did the trick as is and I managed to join the dots.

                  For IP44 the circuit breakers must be covered, not open - but the cover doesn't have to be tightly sealed at the joint to the db (which would make it IP55)