Distribution board over toilet
Collapse
X
-
Distribution board over toilet
Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services -
I suppose it is a smelly situation.Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.zaComment
-
As far as I know it wouldn't breach the regs apart from maybe being easily accessible for emergency supply isolation if the cubicle/bathroom is in use and locked._______________________________________________
_______________________________________________Comment
-
After some careful thought, we're going to apply
6.6.1.7 A distribution board shall not be mounted
c) within a radius of 1m from a water tap or valve (in the same room), unless the enclosure provides a degree of protection of at least IP44.
The next question, given the design - would it be acceptable to insert a rubber strip to seal the door edge against the cover?Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene ServicesComment
-
Hmm, I thought the sink was 2 meters away so you must be referring to the toilet flush...which is plastic. To be honest I suspect the enclosure might be IP 44 as it stands even without a rubber door gasket. All the panels with door gaskets that I have in my stock are IP55 or better, I just checked. From what I can see in the photos I would just take a laissez faire stance on this one and give it the benefit of the doubt.
_______________________________________________
_______________________________________________Comment
-
Yep - it's the toilet cistern refill valve I'm concerned about. And I believe requiring IP44 is fair enough to cover water flying around if something went faulty there.
Thanks for that guidance - very helpful.Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene ServicesComment
-
Nope, the photos did the trick as is and I managed to join the dots.
For IP44 the circuit breakers must be covered, not open - but the cover doesn't have to be tightly sealed at the joint to the db (which would make it IP55)Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene ServicesComment