I got a client who asked me to install LED back up fittings at their complex. I installed the fittings below the electric fence cable which runs in a pvc conduit pipe. When the mains power is on everything works as it should but as soon as there is load shedding and the lights must come on at 30% of its brightness the lights is starting to flicker when the fence is pulsing. Any idea what I can do to prevent it from happening?
Electic fence interfer with led fitting
Collapse
X
-
Tags: None
-
Electric fences do give off inductance or what ever it's called. So it's sending voltage through the airgap and the cables are picking up the voltage.
I am not sure how to fix it perhaps use shielded cable or braided cable to feed the LED and perhaps earth the braided sheath.
Sent from my CPH2197 using Tapatalk -
Thanks but the fitting and the led casings are all plastic so there is no place to connect the earth. Are you saying that I need to connect the one end of the supply cable earth feeding the light to the main earth of the house?Comment
-