Results 1 to 4 of 4

Thread: Earth Tag as Earth Continuity Conductor

  1. #1
    New Member
    Join Date
    May 2020
    Location
    George
    Posts
    1
    Thanks
    3
    Thanked 0 Times in 0 Posts

    Earth Tag as Earth Continuity Conductor

    I have read in the regs, Pg 170 the Note above 6.12.1.5, that the armouring on a cable can be used as an Earth Continuity Conductor.

    Can an earth tag be used as a way to use the armouring as an ECC as well?

    Sent from my Redmi Note 9S using Tapatalk

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    An ECC cable has tinned copper strands ... a plain cable doesnt have any tinned copper cores.

    I have seen sparkies usea copper bonding strap around the wire armouring ... personally I would never do it.
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. Thanks given for this post:

    Matt.24 (02-Oct-21)

  4. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Hi
    You can use a earth tag to increase the contact area and create a better earth path.The note on 6.12.1.4 allows for that as you alluded to.

    You would still need to verify that the resistance values are correct.

    Do not mix up a normal armour cable vs an ECC armour cable where a section of the armouring is replaced with tined copper wires .
    The ECC cable is covered under 6.12.1 b and d - Ecc manufactured cable is manufactured to a specification and the tined copper wires are designed to comply with SANS 10142-1 for the cable amp rating as supplied by the manufacture

    Pasted both regs below for ease of reference



    6.12.1.4 An earth continuity conductor may have branch circuits provided that
    the selection of the conductor size follows the requirements in table 6.28(a)
    and 6.28(b) with due consideration to the maximum length from the upstream
    protective device.
    NOTE The information in 6.12.1.4 also applies to wire armouring if it is used as the
    earth continuity path provided it meets the comparable resistance values of the
    equivalent earthing continuity conductor and the armour wires are all correctly
    terminated using an earthed metal captive coned gland; it may be necessary to replace
    some of the steel wires with tinned copper ones or to use a supplementary earth
    continuity conductor.



    6.12.1 Earth continuity conductors
    6.12.1.1 An earth continuity conductor shall
    a) consist of compatible conductors,
    b) if it forms part of a cable other than a flexible cable, comply with the relevant
    requirements of the standard for the cable,

    c) if it forms part of a flexible cable, be of the same material as, and have a
    nominal cross-sectional area at least equal to, that of the largest phase
    conductor,
    d)be able to carry the prospective fault current without excessive temperature
    rise of the conducor, within the disconnecting time

    e) if it does not form part of a cable or flexible cable, have a nominal crosssectional
    area at least equal to that determined in accordance with
    table 6.28(a), as follows:

  5. Thanks given for this post:

    Matt.24 (04-Oct-21)

  6. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Hi

    Came across a reg that bears relevance to your earth tag question, this morning while looking at Joints

    6.3.7.3 Any armouring or sheathing shall be terminated in or on equipment.
    Armour wires shall be terminated by a clamp or gland in such a way that
    a) pressure is not applied to insulating material, and
    b) there is an earth tag washer (or similar) for connecting to the earth
    continuity conductor.

  7. Thanks given for this post:

    Matt.24 (07-Oct-21)

Similar Threads

  1. Earth continuity conductors
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-21, 01:39 PM
  2. No incoming earth again (and again, and again and again )
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 14-Nov-18, 09:05 AM
  3. Foundation earth
    By Lourie1251 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 27-Nov-17, 07:41 PM
  4. [Question] Using 1 core as an earth?
    By Chilli in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 21-Aug-17, 11:01 PM
  5. [Question] electrical earth continuity
    By Groen Karoo in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 14-Sep-11, 08:07 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •