Results 1 to 4 of 4

Thread: surfix in hazardous areas

  1. #1
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts

    surfix in hazardous areas

    i have always used surfix for lighting in zoned areas. theres very little chance of damage high up. the inspection authority in kuilsriver accept it. however today another master sparky says its illegal as in hazardous areas the earth wire must be the same size as the live conductors.
    any clarification? andy?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Can you calrify what the zoned areas are ie what Division/Zone? I'm guessing you're meaning Ex?
    _______________________________________________

    _______________________________________________

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    From SANS60079
    15.3 Apparatus not requiring earthing
    Where there is no requirement for earthing or bonding, for example, in some types of
    electrical apparatus having double or reinforced insulation, or for which supplementary
    earthing is not necessary, an internal or external earthing or bonding facility need not be
    provided.
    NOTE Double insulated apparatus, while not presenting a risk of electrical shock, may need to be earthed or
    bonded to reduce the risk of ignition.
    15.4 Size of conductor connection
    Earthing or equipotential bonding connection facilities shall allow for the effective connection
    of at least one conductor with a cross-sectional area given in Table 5.

    Click image for larger version. 

Name:	untitled2.jpg 
Views:	525 
Size:	76.8 KB 
ID:	3296

    In addition, earthing or bonding connection facilities on the outside of electrical apparatus
    shall provide effective connection of a conductor with a cross-sectional area of at least
    4 mm2.
    So if the CSA of your live is <16mmsq then the earth must be the same size. This would rule out all domestic installation cables as the earth is invariably one or two CSA sizes smaller than the live and neutral.
    _______________________________________________

    _______________________________________________

  4. #4
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    ex zones yes .
    mmmm, i also see in sans 10086 ,something about "if the required earth conductor size cannot be achieved,the main circuit must be on an earth fault protection system."
    the lights i am doing are on 300 ma earth leakage. all metal equipment are bonded with a 10mm external earth. the lights are plastic of course.

Similar Threads

  1. [Question] Hazardous location Work experience
    By Jacechop in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-Apr-12, 05:00 PM
  2. [Question] Business Problem Areas
    By AmithS in forum Entrepreneurship and Business Management Forum
    Replies: 33
    Last Post: 01-Oct-11, 08:54 AM
  3. [Article] Cable glands for hazardous areas
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 22-Aug-10, 06:13 PM
  4. [Article] OHS Act and hazardous areas
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 0