I Agree with Derlyn
Further to that and a problem that could occur by earthing the earth neutral - How big is the pole top transformer ,
For any of your protective components to operate on an earth fault, your neutral and earth must be at the same potential, so I would suggest earthing
Derlyn Yesterday, 10:36 PMI do the installation as the customer requests and sign the COC, I am yet to have someone challenge me on the silly plug.
You cannot enforce
ELI Way out of Spec
Thanks for the replies. The comments are as expected. I have bridged the earth / neutral in the main DB and left the sub DB's as TN-S. We will just have
RegElec Today, 10:23 AM