You dont need to use PV cables between the combiner and the inverter, the PV cables are double insulated for use on the roof.
Just make
Hi guys, does anyone know who stocks 16 and 25mm PV cables? Inverter max capacity is 80A and I will have 68A to connect between combiner box and inverter.
Sparks Today, 12:52 PMThanks Derlyn. I appreciate the input and I may have to do this as I cannot see Eskom rectifying the problem.
RegElec Today, 12:48 PMIf you hit in a spike at the kiosk and connect to the neutral then the earth spikes on your installation aren't ornaments anymore and the ELI test should
Derlyn Today, 12:04 PM
Neutral/earth bridging method.
I always installed a contactor and selected "Signal islanding mode" before. Installed a 8kW Sunsynk this week and was surprised to find PE/N
Andrew_van_Zyl Today, 07:07 PM