    RegElec

    ELI Way out of Spec

    Thanks Derlyn. I appreciate the input and I may have to do this as I cannot see Eskom rectifying the problem.

    RegElec Today, 12:48 PM Go to last post
    Derlyn

    ELI Way out of Spec

    If you hit in a spike at the kiosk and connect to the neutral then the earth spikes on your installation aren't ornaments anymore and the ELI test should

    Derlyn Today, 12:04 PM Go to last post
    RegElec

    ELI Way out of Spec

    I think I jumped the gun there. I cannot join the earth neutral at the kiosk / meter box as there is no earth there. The supply to the kiosk is via aerial

    RegElec Today, 11:32 AM Go to last post
    RegElec

    ELI Way out of Spec

    Noted. I have access to the meter box so I will see whether it can be done there.

    RegElec Today, 11:22 AM Go to last post
    GCE

    ELI Way out of Spec

    I would rather have done it at the meter box if possible at least then i would not have contravened 6.1.6 and if there is a huge surge down neutral earth

    GCE Today, 10:46 AM Go to last post